S sturnus skrev:
I'm sorry, but that's not true. These types of toilets are designed to be built into the wall. You see them every day, for example, in shopping malls and gas stations. Ask them to show you the regulations.
[bild]
Do you see the nonsense in this drawing that the toilet drain needs to be 70mm from the wall???

And let me ask: did they move the heating cable so it wouldn't reach under the cower? Or did they perhaps have some silly explanation, like that it's needed to defrost the water tank or evaporate condensate?
This is from Säker Vatten. So in order to build them entirly flat in the wall you need to build another wall in front of the regular one.

Ritning av WC med inbyggd spolcistern i våtrum, visar tätskikt bakom toalett och avståndskrav på minst 60 mm från väggen.
Inloggade ser högupplösta bilder
Skapa konto
Gratis och tar endast 30 sekunder
 
So @sturnus whats your comment about the picture above from Saker Vatten? You made a lot of noise however it seems like theyre correct about the 6cm from the wall.
 
Kan vi hålla språket till svenska här? TS förstår uppenbarligen svenska, och den som började skriva på engelska förstod uppenbarligen tråden så att alla andra ska börja skriva på engelska för att en användare skrev ett engelsk inlägg är helt befängt... finns en massa engelsktaliga forum om man föredrar det.

Vad gäller sakfrågan, det finns minimiavstånd till vägg från avloppsrör pga tätskikt, men det går såklart också att dra ett avloppsör som ligger inuti väggen och inte bryter golvets tätskikt, finns också speciella inbyggnadscisterner som får lov att ligga utanför tätskiktet så att det inte behövs någon extra utbyggnad alls.
 
  • Gilla
TobiasStockholm och 9 till
  • Laddar…
@Klockanpå Saker Vatten is just a recommendation. Even in Saker Vatten I don't see that the cistern cannot be mounted in the wall. It's a commercial company that has introduced its own standard to the market. There are also other associations with different recommendations, with different RULES, not LAWS. And if you see such solutions being widely used, you don't think they're allowed. But if you still think that placing a heating cable under a closed space is okay? That the lack of thermal insulation between the ceiling and the screed with underfloor heating is okay? That not embedding reinforcement in the screed is okay? The lack of thermal separation between the heated floor and brick walls is okay? But they have a Saker Vatten certificate. You can rest easy. So you're only confirming what I wrote earlier: You ask, but you know better.
 
  • Gilla
Medvurst
  • Laddar…
A ajn82 skrev:
Kan vi hålla språket till svenska här? TS förstår uppenbarligen svenska, och den som började skriva på engelska förstod uppenbarligen tråden så att alla andra ska börja skriva på engelska för att en användare skrev ett engelsk inlägg är helt befängt... finns en massa engelsktaliga forum om man föredrar det.

Vad gäller sakfrågan, det finns minimiavstånd till vägg från avloppsrör pga tätskikt, men det går såklart också att dra ett avloppsör som ligger inuti väggen och inte bryter golvets tätskikt, finns också speciella inbyggnadscisterner som får lov att ligga utanför tätskiktet så att det inte behövs någon extra utbyggnad alls.
Vi har en vanlig fixtur, då gäller väl bilden enligt ovan och deras installation är helt korrekt?
 
K Klockanpå skrev:
Vi har en vanlig fixtur, då gäller väl bilden enligt ovan och deras installation är helt korrekt?
Det tror jag, även om jag inte tycker det är den bästa lösningen, men jag är bara amatör
 
  • Gilla
Klockanpå
  • Laddar…
S sturnus skrev:
@Klockanpå Saker Vatten is just a recommendation. Even in Saker Vatten I don't see that the cistern cannot be mounted in the wall. It's a commercial company that has introduced its own standard to the market. There are also other associations with different recommendations, with different RULES, not LAWS. And if you see such solutions being widely used, you don't think they're allowed. But if you still think that placing a heating cable under a closed space is okay? That the lack of thermal insulation between the ceiling and the screed with underfloor heating is okay? That not embedding reinforcement in the screed is okay? The lack of thermal separation between the heated floor and brick walls is okay? But they have a Saker Vatten certificate. You can rest easy. So you're only confirming what I wrote earlier: You ask, but you know better.
What do you mean with ”Even in Saker Vatten Idont see the cistern cannot be mounted in the wall”. You can litteraly see in the picture i attached that it cannot be mounted in the wall, unless you build another wall in front of it.

Kan någon på forumet bekräfta om denna person bara trollar eller om den har något fog för sina påståenden?
 
S sturnus skrev:
@Klockanpå Saker Vatten is just a recommendation. Even in Saker Vatten I don't see that the cistern cannot be mounted in the wall. It's a commercial company that has introduced its own standard to the market. There are also other associations with different recommendations, with different RULES, not LAWS. And if you see such solutions being widely used, you don't think they're allowed. But if you still think that placing a heating cable under a closed space is okay? That the lack of thermal insulation between the ceiling and the screed with underfloor heating is okay? That not embedding reinforcement in the screed is okay? The lack of thermal separation between the heated floor and brick walls is okay? But they have a Saker Vatten certificate. You can rest easy. So you're only confirming what I wrote earlier: You ask, but you know better.
Du förstår tydligen svenska, kan du inte då anstränga dig att svara på svenska?
 
  • Gilla
  • Wow
Jorel03 och 3 till
  • Laddar…
K Klockanpå skrev:
What do you mean with ”Even in Saker Vatten Idont see the cistern cannot be mounted in the wall”. Y
Webbsidan visar branschregler för installation av WC med inbyggd spolcistern, med text om läckage, placering och materialkrav.
Inloggade ser högupplösta bilder
Skapa konto
Gratis och tar endast 30 sekunder

K Klockanpå skrev:
Kan någon på forumet bekräfta om denna person bara trollar eller om den har något fog för sina påståenden?
The basis for my claims is on the SV website above. But since I know some people have trouble reading with understanding (like children), I'm including a drawing (like in children's books). I'll also add a description to make it easier to understand. The blue one is the waterproofing. The transparent, reddish one is the built-in cistern cover. At the bottom is the drainage gap I wrote about a long time ago. Once built, it won't be transparent. This is just for you. :-D Show these "experts" that there's no need to waste half a meter of bathroom space on such they built-ins. And as I mentioned earlier, you can still straighten it out.

3D-teckning av ett badrum, med blå vattentätning på väggar och golv, röd inbyggd cistern, och dräneringsgap vid botten.
Inloggade ser högupplösta bilder
Skapa konto
Gratis och tar endast 30 sekunder

and sectioncut
3D-diagram av ett hörn i ett badrum. Den blå ytan visar vattentätning, den transparent rödlila ytan visar en cisternfront. Visar även ett dräneringsutrymme.
Inloggade ser högupplösta bilder
Skapa konto
Gratis och tar endast 30 sekunder


And I wrote about this a long time ago in your thread, but as I wrote earlier: you ask but you know better
https://www.byggahus.se/forum/threa...m-ser-det-bra-ut-hittills.569598/post-6541125
The way it was built is one thing, but the errors I mentioned are another. You somehow didn't address them. I mentioned earlier that I suspected some group had found you to be a cash cow. Now I'm starting to suspect you're trolling and this is your own job. And that's all for this thread.
 
Redigerat:
  • Gilla
Medvurst och 2 till
  • Laddar…
Immobil Immobil skrev:
Du förstår tydligen svenska, kan du inte då anstränga dig att svara på svenska?
You're wrong, unfortunately, I don't know. And I know that Google Translate sometimes makes terrible mistakes when translating into Swedish, which can change the meaning of a sentence. That's why I prefer to use a language I can verify. But I can write in Polish if you prefer ;-D
 
  • Gilla
Testarn och 5 till
  • Laddar…
Bilderna i inlägg #136 visar väl att det behöver vara minst 60 mm mellan avloppsrör och tätskikt.
För om du fortsätter läsa i samma paragraf så nämns prefabricerade tätskiktskonstruktioner och en bild på spolcisternen bakom tätskiktet.
Så visst går det att ha spolcisternen inuti väggen utan att bygga en ny vägg, om rätt material används.

https://www.gvk.se/branschregler/toalett-eller-bide/vagghangd-toalett/

Illustration av cistern bakom tätskikt med avloppsrör och minst 60 mm avstånd till tätskikt enligt byggstandard för väggmonterad toalett.
Inloggade ser högupplösta bilder
Skapa konto
Gratis och tar endast 30 sekunder
 
  • Gilla
grovspacklarn och 2 till
  • Laddar…
Pjosk75 Pjosk75 skrev:
Bilderna i inlägg #136 visar väl att det behöver vara minst 60 mm mellan avloppsrör och tätskikt.
För om du fortsätter läsa i samma paragraf så nämns prefabricerade tätskiktskonstruktioner och en bild på spolcisternen bakom tätskiktet.
Så visst går det att ha spolcisternen inuti väggen utan att bygga en ny vägg, om rätt material används.

[länk]

[bild]
Tolkar du det som att det är hantverkaren som behöver bygga ett tätskiktsutrymme för att bygga in fixturen eller att man behöver köpa en särskilt fixtur som kommer inbyggd i en prefabricerad tätskiktskonstruktion?
 
Tätskiktskonstruktionen behöver köpas färdig eftersom den ska vara testad och godkänd.

Geberit har visst en egen produkt för detta. Men det är väl svårt att använda den nu när avloppet redan är fast gjutet i golvet framför den befintliga väggen.

https://www.geberit.se/rorsystem-in...tallations-och-spolsystem/geberit-duofix-tek/

Fixturen på bilden i länken ovan ser ut att vara lik den du själv länkade till tidigare.

Tillägg: Det kan vara en egen fixtur för övrigt som passar mellan träreglarna.
 
Pjosk75 Pjosk75 skrev:
Tätskiktskonstruktionen behöver köpas färdig eftersom den ska vara testad och godkänd.

Geberit har visst en egen produkt för detta. Men det är väl svårt att använda den nu när avloppet redan är fast gjutet i golvet framför den befintliga väggen.

[länk]

Fixturen på bilden i länken ovan ser ut att vara lik den du själv länkade till tidigare.

Tillägg: Det kan vara en egen fixtur för övrigt som passar mellan träreglarna.
Detta är den vi har köpt: tror inte den funkar för helt inbyggd i vägg?

https://www.vvsochbad.se/geberit-du...&utm_medium=cpc&utm_campaign=price-comparison
 
Så det enda suturnus egentligen gapar om är att vi hade kunnat bygga in den, om vi hade köpt en annan fixtur?
 