I was going to check how many leaves were on the roof after the fall. I discovered that almost all of the battens and the ridge board were moldy.

The counter battens seem to have held up. The wood under the plastic looks like new.

The roof was built by me last summer as follows:

Vapor barrier
195 mm insulation
3 mm oilboard
25 mm air gap, open to the ridge throughout the building
22 mm tongue-and-groove boards
T-emballage Evo roof membrane
25 mm counter/battens
Concrete tiles

The ridge is ventilated from the inside (open at the ridge) and with a vent ridge. I looked as far as I could into the air gap between the board/tongue-and-groove boards and couldn't see any growth.

Roof ridge with exposed battens and clear plastic, showing underlying materials and metal sheets, amidst a green garden background. Close-up of a wooden roof board with visible mold growth along the edge.

What happened?
 
Even the space under the roof tiles needs ventilation. The ridge board probably doesn't like the plastic on the top side either. It's hard to say more without having seen a section over the ridge.
 
Replace point 1 with Benders ventinock. That's how the roof looks. Cross-section diagram of a roof ridge with labeled components, showing a Benders vent ridge and where the ridge board should be under plastic.
In the picture in the first post, the ridge board is removed. It is therefore not mounted under the plastic. However, under the ventinock plastic.

I forgot that I also have a glulam beam in the middle. But that doesn't matter for the function.
 
K
Is it not the case that humid indoor air is passing through the vapor barrier in any way? If it condenses on the battens, it will lead to mold..
 
  • Like
rererere
  • Laddar…
I inspectah44 said:
In the picture in the first post, the ridge board is removed
OK. The root cause is obvious; it's too high relative humidity under the tiles. Since the plastic lies on top of the counter batten and just under the topmost supporting batten, the air under the tiles doesn't escape. The relatively low roof pitch doesn't help. Surely, you haven't used a diffusion-open roof membrane?
 
The slope is about 22 degrees and no diffusion-open membrane has been used. The length from the foot to the ridge is just under 4 meters.

I don't understand how the air under the tiles couldn't have escaped. It's "open" all the way to the ridge board and further out through the vent ridge plastic.

Could the airflow from the tongue-and-groove ventilation have disrupted the flow from the eaves to the ridge?

The question is whether it helps to have a narrower strip of plastic over the ridge hole so that the air can move upwards more easily? Because I have to have some kind of protection over the hole.

Strange that the counter battens have fared well!
It doesn't feel particularly good that there is already mold, but I guess I'll have to keep an eye on it and live with it.
 
I inspectah44 said:
Strange that the scattered rafters have survived!
It is logical. They are located lower down. Mold in cold attics always occurs on the underside of the roof sheathing, not on the rest of the roof structure. You need to find a way to better ventilate under the tiles. A 22-degree roof pitch is practically inadequate in combination with concrete tiles. Seamed tiles are theoretically supposed to handle 20 degrees, but that's theoretical. The rather long roof span of 4 m also contributes.
 
How do you mean that the battens are lower? They're pretty much attached to the load-bearing battens? I haven't seen any growth on the underside of the raw plank. Yet at least. Close-up of roof battens and wooden boards, possibly part of a ventilation system under concrete tiles.
Regarding the slope, Benders states that the minimum slope is 14 degrees on their concrete tiles.

I think I will, as I mentioned earlier, reduce the plastic strip and make the holes in the ridge vent larger. I'll replace the ridge board with a new one and see if it makes any difference. Ventilation ridge with circular holes used in roofing for airflow and preventing moisture buildup.
 
The water vapor condenses on the material that is coldest. The batten is colder than the counter batten. When Benders specifies 14 degrees as the minimum slope for their concrete tiles, they are making a short-term assessment. If concrete tiles are to last long, they should have a much greater roof slope. I think it's false advertising. If you increase the ventilation under the tiles, the problems will be resolved. So far, nothing serious has happened, you have just received a warning.
 
  • Like
Jesper Ronn and 1 other
  • Laddar…
Now I understand what you mean. ;)
Thank you for taking the time to help.
 