Hello.
The electrician suggests 5x2.5 as supply to the Attefall house. It will be a small residence; llvp, washing machine, water heater, fully equipped kitchen, etc. There is 25a in the facade meter cabinet, and the supply to the concerned cabin is 50 meters. Will it be enough, do you think? 16A, that is. Thanks in advance!
The electrician suggests 5x2.5 as supply to the Attefall house. It will be a small residence; llvp, washing machine, water heater, fully equipped kitchen, etc. There is 25a in the facade meter cabinet, and the supply to the concerned cabin is 50 meters. Will it be enough, do you think? 16A, that is. Thanks in advance!
I would say it feels so-so. 50m is long, you may have problems with 16A being a bit too weak. 16A is probably the max you can secure that cable. You will probably also not meet the requirement for the maximum allowed voltage drop. No need to use 2.5, use 6mm2 instead.
Construction veteran
· Stockholm
· 340 posts
That was my concern. Go with 6 unless someone else has a different opinion/knowledge? Big thanks!J Johan456 said: