Hello! The company that built the leca foundation (8m2) for our extension did not leave holes for ventilation (because I told them I would have vents in the hatches which I later changed), so I thought about drilling/sawing my own and installing vents.

But the vent grilles I want to use are square, and I can't find any square ducts.

I'm wondering if I really need a duct, or if I could just plaster the inside with a hard cement mortar?

The vents are of the type that are plastered in:
Square metal ventilation grille with horizontal slats, designed to be plastered into walls for ventilation purposes.
 
L
Not common with pipes through foundation walls, just a hole with a vent on the outside
 
Claes Sörmland
Exactly, plaster
A Alko said:
Considering if I really need a duct, or if maybe I can just plaster the inside with a hard cement mortar?
[image]
That's how it usually looks!
 
Sounds good, thanks for the reply!
 