I don't think the lower option can withstand the wind forces when it presses on the roof and wall from the right in the image.

The standing yellow beams will buckle in the middle from the pressure forces from the blue.

It might work if the truss is very securely attached to the brick wall so that YELLOW-BRICK WALL-TRUSS forms a rigid triangle, but there will still be very large pressure forces across the yellow.

Appealing solution otherwise.
 
mycke_nu. A majority of the country's log buildings are constructed in a similar manner. If you want to be completely sure about how the forces in the constructions are distributed and how large they become, you must sit down and calculate the frame (pencil and paper or e.g. pcframe). My advice to hire a designer to determine the dimensions therefore remains firm.
 
Clearly, that's why I wrote think. :)
 
S
Okay, I've made some progress. What do you think?
Next up is building new walls and cutting the beams.

A partially constructed building with exposed wooden beams and a roof structure, awaiting new walls and beam trimming.
Roof construction with wooden beams, awaiting wall installation and beam cutting, progress of a building renovation project.
Wooden beams forming a cross pattern in an unfinished structure with corrugated metal walls, showing construction progress.
An unfinished attic space with exposed wooden beams and insulation visible, showing progress on a renovation project to build new walls and trim beams.
 
The question is whether the wood can withstand the edge pressure from the bolts, especially at the ends towards the roof trusses. The risk is that the wood splits and the bolts slip out. However, it's not my area, so maybe someone else can offer insights.

Spontaneously, it feels like there should be more bolts or metal reinforcement around them.
 
Apart from what mycke_nu mentions about the number and execution of anchoring points, I wonder why you haven't brought together the lower horizontal with the legs in the scissors?
 
S
GK100 said:
In addition to what mycke_nu mentions about the number and execution of anchor points, I'm wondering why you haven't brought together the lower horizontal with the legs of the truss?
Okay, I've bought some bolts to attach the lower tie beam with the trusses.

I will review if I should increase the number of anchor points, what is currently there is:
16mm threaded rod
Washers 50mm x 5mm
Nuts

The studs are 220x45
 
I think it looks good, really sturdy, better to go a bit extra while you're at it. Just like mycke_nu wrote, I would probably have doubled up at the ends near the rafters, but that's mostly intuition. More important might be how you secure the fittings at the lower points.
 
S
Okay, now I've played Tarzan between the rafters and placed bolts between the lower beam and the scissor.
Wooden trusses and beams in a roof structure, secured with bolts and steel supports, showing reinforcement work on the roof's lower truss and rafters.

Custom-made a bunch of steel to anchor the scissors to the wall. One on each side and two threaded rods that bind them together.
Metal straps bolted to a wall and rafters in an attic, used for securing structure, with threaded rods connecting components.

Is it approved now, I wonder? :)
 