I have started looking into glulam again. I found a secondary beam that I think suits me, it is 56x180 but unfortunately, it's not a standard size so it is not included in the calculation program at Swedish Wood.
How long can it be at most between the load-bearing beams?
Max deflection 8 mm
Cc 1015 between secondary beams.
Roof slope 5 degrees
Snow zone 2
Roof weight 0.27 kN
If I enter the dimensions into the calculation program, the maximum span for 42x180 is approximately 2850mm at 8mm deflection (L/344)
I've started looking into glulam again. I found a secondary beam that I think suits me, it is 56x180, but unfortunately, it is not a standard dimension, so it is not included in the calculation program on Svenskt Trä.
How long can it be at most between the load-bearing beams?
Max deflection 8 mm
Cc 1015 between the secondary beams.
Roof slope 5 degrees
Snow zone 2
Weight roof 0.27 kN
If I enter the dimensions into the calculation program, the max span for 42x180 is approximately 2850mm at 8mm deflection (L/344)
Depends on what strength and stiffness properties you have. For GL28cs, you get a final deflection of 8 mm with 56x180, L = 3m, and your other mentioned parameters.
It is not entirely straightforward to calculate such a connection as you have contributing strength from both the glue and the screw. A detailed calculation of that specific connection is required (which I currently do not feel like doing). You will get less than 8 mm in any case.
Another option is to use 45x145mm in the highest possible class, maybe get a hold of C30 or C35. Then I can reinforce with flat iron 6x140mm on one side of the beam.
I have thought about it and decided to construct the entire structure with glulam beam 90x180. It's going to be a big build. It would be really nice if someone could take a wise look at the drawing and provide feedback.
I entered the data into svenkt trä and got the following:
The height I have to work with is 430 mm and then it becomes:
180 primary beam
180 secondary beam
26 profile
Then the secondary beams are at an angle, so they rise a few cm behind the primary beam. Additionally, I need a few cm to attach the sheet to the existing eaves.