I'm working on building a house and have a glulam beam that rests on two nail-laminated 45x95 on one end and three nail-laminated 45x95 on the other end.

I went to check it out yesterday and noticed that the stud beams that are nail-laminated are not cut straight. This means that the studs, which become load-bearing pillars, actually only have contact surface against roughly one 45x95 at each end.
See the pictures in the post for how it looks.

Should I demand that this be redone, or am I just being overly picky?

The carpenter says that it's enough to put in a wedge so that it aligns with all the posts. Is that really enough?

He also says that "as long as you're not planning to have an excavator on the upper floor, it's fine."

What should I do?
 
  • View of a glulam beam resting on skewed joined studs, with visible gaps and nails, displayed in a construction setting.
  • Close-up of wooden beams with uneven cuts, supporting a laminated beam. The focus is on the alignment and surface contact of the beams.
  • Close-up of two unevenly cut, nail-glued wooden beams of 45x95 size, forming a column supporting a glulam beam in a house construction project.

Best answer

U
Excessively finicky
 
  • Like
foppa and 6 others
  • Laddar…
That's not a problem.
 
When pressure is applied to it, it becomes smooth.
 
  • Like
Appendix
  • Laddar…
H
Wedge that in on the little one I think will be difficult.
No, like before, that's no problem.
 
Wood is a living material still. Even if it had been 100% surface today, it is not certain it will be the same tomorrow so to speak.
 
  • Like
Appendix
  • Laddar…
P
Thank you so much for so many quick responses! Now I can feel calm! This forum is fantastic in that way ☺️

The carpenter sounds so arrogant when I've talked to him about it. It sounds like he got irritated just because I even asked.. Therefore, I became a little skeptical.

Can I also be calm about the wedges they placed under the floor joists against a load-bearing wall? The nogging in the wall has become the same height as the bottom of the glulam beam, but it should actually be 10 mm higher. Therefore, they have inserted wooden wedges that are 10 mm, it feels like they are really tight and secure. Is that also an okay way to do it?
 
U
Henrik_z said:
Thank you so much for so many quick responses! Now I can feel at ease! This forum is fantastic in that way ☺️

The carpenter sounds so arrogant when I've talked to him about it. It sounds like he got annoyed just because I even asked... Thus, I became a bit skeptical.

Can I also be at ease with the shims they placed under the floor joists against a load-bearing wall?
The top plate in the wall has become the same height as the underside of the glue-laminated beam, but it should actually be 10 mm higher.
That's why they've put in wooden shims that are 10 mm, it feels like it's really tight and good.
Is it also an okay way to do it?
hard to say without a picture
 
P
U Utsliten och utdömd said:
difficult to say without a picture
I'm trying to upload but only get an error..
 
P
Here's the image
 
  • Close-up of wooden construction framing with visible boards and OSB, featuring hand-drawn marker lines for measurement or cutting guidance.
P
Is the wedge between the load-bearing wall and the floor joist OK too? ☺️
 
U
Yes, that's not a problem either. However, I would have used plastic spacers or something similar to avoid the risk of it cracking. But I wouldn't redo that, it looks good anyway :)
 
  • Like
Appendix
  • Laddar…
P
U Utsliten och utdömd said:
Yes, that's not a problem either. However, I would have used plastic spacers or something similar to avoid the risk of it cracking. But I wouldn't redo it, it still looks good :)
Thank you so much for the reply, now I can continue sleeping soundly! ☺️
 
Best answer...
He also says that "as long as you're not going to have an excavator upstairs, it will be fine."
 