Hello, I am in the process of renovating our house from 1973.

I have a wall that we want to remove. So I thought I’d do it with you if you can help me calculate what size VKR beam is needed.
Ideally, I would like to embed the beam in the wooden joists a bit to get a smooth ceiling.
As this gentleman has thought:
https://www.byggahus.se/forum/threads/faella-in-vkr-balk-i-traebjaelklag.132894/

Currently, there are 70x70 studs distributed over 4 pieces.

The length of the VKR beam will be 263 cm
The span of the wooden joists is 850 cm
The wooden joists are 45x195 cm
The house is 1.5 stories with a basement.

Floor plan sketch showing beam layout and dimensions for a house renovation, with a red arrow highlighting a specific area for VKR beam consideration. Floor plan of a house with labeled rooms and a pencil pointing at a bedroom. Rooms include a 9 m² and 7 m² bedroom, 28.5 m² living room, kitchen, and hall. Interior room under renovation with exposed framing and wooden beams, visible window, ceiling lamp, and tools on the floor.
 
  • Blueprint showing the layout of an attic with rooms labeled "Sovrum" (bedroom) and areas marked for storage.
  • Blueprint of a house basement floor plan, showing rooms labeled as "Bastu," "Pannrum," with hand-drawn markings and notes in blue ink.
  • Floor plan of a two-story house with proposed wall removal; includes kitchen, living, and dining areas. Highlighted area shows where a VKR beam might be placed.
Last edited:
Do you have any more drawings, of the foundation and any section. Is it an upper floor or the roof that the beam is supposed to support?
 
B bossespecial said:
Do you have any more drawings, of the foundation and any section. Is it an upper floor or roof the beam is supposed to support?
I have added pictures and information in the thread starter.

The house is a 1.5-story with a basement, the beam is supposed to support the upper floor.

If there are any more drawings you are missing, just let me know. I have all the original drawings of the house.

Sorry for the messy thread start.
 
A section with dimensions and information on the snow zone is also needed to calculate the loads. Why do you want an VKR beam? They are not intended for that size of loads that are relevant. Embedding the beam in the floor is less suitable because the joists are joined over the wall. Additionally, it's unnecessarily complicated.
 
  • Like
BirgitS
  • Laddar…
J justusandersson said:
You need a section with dimensions and information about the snow load zone to calculate the loads. Why do you want a VKR beam? They are not intended for the size of loads that will be relevant. Embedding the beam in the floor structure is less suitable since the joists are joined over the wall. Additionally, it is unnecessarily complicated.
I think a VKR beam is more compact than a glulam beam.

But I agree with you that it is a bit more complicated work. However, if it works, it's the neatest, and you get a smooth ceiling.

Is the alternative to use a glulam beam in an appropriate size?
 
A more efficient (and suitable) steel profile is, for example, an HEA profile. It is much stiffer and stronger than a VKR profile of the same height. As mentioned, it's a relatively extensive operation to recess the beam, but I agree that a smooth ceiling looks much nicer. Personally, I would have made it more complicated and hidden the beam in the ceiling(y)
 
B bossespecial said:
A more efficient (and suitable) steel profile is, for example, an HEA profile. It is much stiffer and stronger than a VKR profile of the same height. As mentioned, it is a relatively extensive operation to recess the beam, but I agree that a smooth ceiling looks much nicer. Personally, I would have complicated it and hidden the beam in the ceiling(y)
How would you go about complicating it and hiding the beam? And what dimension of the beam would you aim for?

I'm just a happy hobbyist trying to learn:p
 
A small miscalculation, it's difficult to fit an I-beam since the flange is in the way:p
One could create a combination of an as narrow as possible rectangular VKR on the plate and a T-profile that is inserted into the floor structure. You should check that the floor structure and truss work when cutting the overlap. You could also check how much it is appropriate to notch out the beams at the bottom. That way, you could raise the VKR somewhat and then lower the suspended ceiling to remove it.
 
The beams are probably rigidly spliced. I don't think one should put the compensating beam in the floor structure. I don't find it particularly disturbing to have a beam in the ceiling. I never go looking for errors in the ceiling, perhaps it's an age symptom...
 
  • Love
kulle
  • Laddar…
A good start is to check if the beam system works even if the overlap is broken. If the answer is no, one should consider if it's worth needing to reinforce the beam system just to fit in the beam.
Hopefully, it's an age symptom because I'm starting to get neck issues from looking at ceilings and searching for all visible deflections:p
 
One should always ask whether the measures are reasonably proportionate to the benefit. I can see a point in removing the wall in this case.
 
Exactly, it makes a big difference if the wall is removed. The idea is that it should become part of the kitchen.

Do you have to hire an engineer to calculate it?
What I mean is that a beam of 2.7 meters is not very long. So maybe you can, with both belt and braces, say that, for example, a HEA180 beam would work perfectly for the purpose?
 
It is not a good idea to guess as long as all conditions have not been clarified. The difference between the highest and lowest can be significant. A sectional drawing and information about the snow zone is a good step on the way.
 
BirgitS
R Rise said:
Do you have to hire an engineer to calculate it?
You need to submit a building notification for Interventions in the load-bearing structure and depending on the municipality, it may be required to show a calculation on how to size beams and pillars.
 
J justusandersson said:
It is not a good idea to guess as long as all conditions are not clarified. The difference between the highest and lowest can be significant. A sectional drawing and information about the snow zone are a good step in the right direction.
J justusandersson said:
It is not a good idea to guess as long as all conditions are not clarified. The difference between the highest and lowest can be significant. A sectional drawing and information about the snow zone are a good step in the right direction.
Hello again. It has been a while:p
We live in the Gothenburg area. So it is snow zone 1.5
Here are some Sectional Drawings. I hope they are satisfactory.
Blueprint section drawing showing structural measurements and dimensions for a building project, including labels for various beams and panels.
Blueprint section drawing of a house labeled "SEKTION A-A" showing structural dimensions and room divisions, including roof slope and measurements.
Cross-section architectural drawing for a building project, detailing structural measurements and design elements such as angles and beam specifications.

I have talked to a friend who is a Construction Engineer working in construction operations. He said that an HEB200 works.
So I've been pondering and thinking about how to proceed to make it look the best. I found an existing thread on byggahus
how he did it.
So I think it should be possible to do the same but instead of just putting a flat iron at the bottom that the joist rests on, I will weld on a custom-made joist hanger in the Heb200 beam. So that you can fasten the joist properly and it can't twist.

I attach link and pictures:
https://www.byggahus.se/forum/threads/limtrae-v-s-jaernbalk.167190/page-2

Metal beam installation with a custom-made beam shoe on an HEB200 beam, connected to wooden joists and surrounded by pipes in a construction setting.
Wooden floor joists with insulation and exposed pipes, showing construction details for a joist hanger or connection in a renovation project.
 