Noramasen Noramasen said:
A downright deplorable job. If one is completely without professional pride or knowledge, they would leave an execution like this. There are many points of critique, but the most important errors that absolutely shouldn't be present, and which must be pointed out to the company, are:
  • The so-called plaster edge where the execution is completely wrong. A proper plaster edge should consist of a "shelf" that is overbent at about 110º (with fold) so that if the plaster later comes apart, the water will run from the chimney and not into it. And there should NOT be any joint there as the plaster does not adhere to it.
  • Left a fold without a binding which can seriously injure someone. And this binding should occur under the plaster edge.
  • All sides should meet at their corners, otherwise, there will be different heights on the sides when the plaster is applied.
  • If applying plaster to the chimney, for heaven's sake, there should not be any visible screws of mounting type, but hidden attachments with clips.
  • And the same goes for the seam type of cuts in corners. It should be of a curved type.
Furthermore, it's hard to tell what type of black flashing it is despite the description, but regardless of how exposed the situation is, it doesn't look good. Feel free to take a picture from a bit further away, and it may become clearer, allowing for alternative solution suggestions.
Kind regards/Masen
The new one was better... but nice?
Noramasen; I've "heard" that if you put together 2 sheets, they should be folded 3 times. Do you know anything about that?
 
  • Like
jorgen60 and 2 others
  • Laddar…
R.Wallin R.Wallin said:
The new one was better...but stylish?
Noramasen; I have "heard" that if you put together 2 sheets, they should be folded 3 times. Do you know anything about that?
2 times for a double seam
1 time single seam
 
  • Like
R.Wallin
  • Laddar…
J jliljeha said:
If it was the same tinsmith who did that, one might wonder what happened on the first attempt.
Yes, it's the same guy. My partner works from home, so she's seen him. Don't know what happened the first time though. :thinking:
 
  • Like
  • Wow
R.Wallin and 1 other
  • Laddar…
J Joakim88 said:
Yes it's the same guy. My partner works from home so she has seen him. However, I don't know what happened the first time. :thinking:
"My partner works from home so she has seen him. However, I don't know what happened the first time. :thinking:"

The plåtis might have been in a rush last time. Why, only the plåtis and the partner know... :rofl:

Joking aside! Now I think you can be satisfied. It looks good. And you've placed the ridge tape correctly. (y)
 
  • Haha
  • Like
Huddingebo and 3 others
  • Laddar…
J Joakim88 said:
Then any water still runs in under the tiles. :thinking: It should lie over the ridge board and out onto the upper edge of the tiles, according to what I have understood anyway.
There is red!
 
M mats.r.nilsson said:
There is red!
There absolutely is. But I bought the wrong one and don't think it matters that much. :p
 
J Joakim88 said:
Had a tinsmith here at home today. We're getting various things done on the roof and he started with the lower flashing on the chimney. The chimney will be plastered later so this should be a flashing with a "putskant".
Since he also started on the dormer, I assume he considers himself done with the lower flashing.

I admit I've never seen a lower flashing up close, but I must admit I was disappointed when I saw what was installed on our chimney when I came home. Is it supposed to look like this? (the picture with black metal is on the flashing above the dormer window)
Not many right!
Take a look at www.teknikhandboken.se
There is professional information about metal as well as detailed pictures of execution for respective building parts taken from AMA hus.

Regards, Tom
Responsible for control according to PBL
Certified construction inspector
 
  • Like
R.Wallin and 1 other
  • Laddar…
T Tooompaaa89 said:
Not many right!
Check out www.teknikhandboken.se
There you will find professional info about sheet metal and detailed images of the execution for each building part taken from AMA house.

Best regards, Tom
Inspector according to PBL
Certified construction inspector
Thanks!
What do you think about the new fitting that I uploaded pictures of then? :)
 
J Joakim88 said:
Thanks!
What do you think about the new fitting I posted pictures of? :)
Looks good, the upcoming trim/finishing edge will be all the more important. I assume they will fold the trim together with the end of the top fitting and then finish with a plaster edge.. Try to figure out how thick the plaster will be, as the edge on the flashing should be the same. See picture and arrow
 
  • Diagram of wall construction with fastening details and arrows pointing to specific joint areas for plaster application.
  • Like
UffePlåtis and 1 other
  • Laddar…
F fribygg said:
I understand very well that you need roof safety if you're going to sweep from above, but it's a shame to install in a way that mars an otherwise beautiful roof.
There are many standards for chimney sweeping that our municipality has become very strict about since they changed inspectors:
  • The ladder must hang on step irons.
  • Steps on the roof must go straight up to the chimney. No diagonal or horizontal part may occur.
  • Step(s) on the chimney must be permanently mounted. It must have a ladder. You must be able to attach a harness/safety line at the very top.
  • There must be a platform at the top where the chimney sweep can stand.
It became so much with this that we hired a sheet metal shop with this task. After a lot of hassle between the municipality, the company, and the ladder manufacturer, it was finally approved. It became some kind of example for type approval and we got it for free (13’ with platform). It looks more or less like the picture but a little uglier. However, we've placed the platform so it can't be seen from the street. We were, however, forced to have the roof step irons on the front for the above reason.

If you don't fix this on your old house, chimney sweeping will not be approved for professionals. A neighbor has instead taken a chimney sweep course, but I'm skeptical if it's enough as he still can't get the chimney installation itself approved.
 
  • Like
Johan Sahlin
  • Laddar…
elpaco elpaco said:
There are many norms for chimney sweeping that our municipality has become very strict about since they changed inspector:
  • The ladder must be hung on ladder hooks.
  • Ladder on the roof must go straight up to the chimney. Skewing over the roof or any horizontal part is not allowed
  • Ladder(s) on the chimney must be permanently mounted. It must have a leader. One should be able to attach a harness/safety line at the top.
  • There must be a platform at the top where the chimney sweep can stand.
It became so much with this that we hired a sheet metal workshop for this task. After much argument between municipality, company, and ladder manufacturer, it was finally approved. It became some kind of example for type approval and we got it for free (13’ with platform). It looks roughly like in the picture but a bit uglier. However, we placed the platform so that it is not visible from the street. The roof ladder hooks, however, we had to have on the front due to the above reason.

If you don't fix this on your old house, sweeping won't be approved for professional operators. A neighbor has instead taken a chimney sweeping course but I am skeptical if it is enough since he still doesn't get the chimney installation approved.
I wouldn't be able to comply with this as I have a dormer that prevents the ladder from going straight up to the chimney.
How do you solve this if the chimney sweep isn't allowed to move sideways on the roof?
Or do you need to build a platform with railings then?
 
M mattoys said:
I would not be able to fulfill this as I have a dormer that prevents the ladder from going straight up to the chimney. How do you solve this if the chimney sweep is not allowed to move sideways on the roof? Or do you need to build a platform with railings then?
As the builder, you are responsible for ensuring compliance with current roof safety regulations during extensive roof renovations. See bbr chapter 8 Check out https://www.taksakerhet.se/ They have good guidance on what "applies" for small houses.

Regards
 
M mattoys said:
I would not be able to fulfill this as I have a dormer that prevents the ladder from going straight up to the chimney.
How do you solve this if the chimney sweeper cannot move sideways on the roof?
Or do you need to build a platform with railings then?
Sooting from below? Self-cleaning?
 
  • Like
Mangebula
  • Laddar…
M mattoys said:
I wouldn't be able to fulfill this since I have a dormer that prevents the ladder from going straight up to the chimney. How do you solve this if the chimney sweep can't move sideways on the roof? Or do you need to build a platform with railings then?
I don't know the rules by heart, only what was emphatically conveyed to me. For example, I want a small narrow "gangway" horizontally on the backside. But it wasn't approved. So some contraption of the kind you mention is probably needed if the inspector is strict. UNLESS you can pull the rungs from the other side of the roof. That's how we've done it since there is a patio roof made of channel plastic on the backside.
 