More information is needed to be able to calculate it. What will be the largest span of the support beam at the front edge? Where in Västra Götaland is the house located? The snow load varies between 1.5 and 3 kN/sqm.
Span in the front edge? Distance between the posts in the front edge? In that case, it's at most 180cm between.
Live in Skövde.
The patio is not so wide, 170cm. If you lay a beam between each bearer out from the roof in the middle, isn't that enough? Is battens still needed? Why are battens needed? Attaching a picture to show what I mean, but straight. And a bit thicker
If the largest measurement is 180 cm, 45x145 C 24 in the front edge is sufficient. If you want a 110 cm distance between the rafters, it is fine if they are also 45x145 C 24 and if you place bearing battens that are 45x120 C 24 on c/c 60 cm. If you want to reduce the dimension of the bearing battens, the rafters must be closer together.