Hi
Building a bathroom, fully tiled.
I need your advice on the durability of the underlying walls.
Today there is 11mm Masonite on cc60 frame. (70s holiday home)
My plan is to use Fermacell for increased strength vs regular plasterboard.

Will this hold?
Will it also hold for heavier mountings such as a vanity unit?
 
The only thing approved under plasterboard nowadays is OSB or plywood 15mm against the studs...
 
Jonatan79 Jonatan79 said:
The only thing that is approved under plasterboard is OSB or plyfa 15mm against the studs nowadays…
Do you have a link to that? Is it new?

Last time I checked, BKR didn't have anything to say about the underlying board... You were allowed to have single plasterboard even

Fermacell is a good board, holds more than plasterboard, but you should have noggins where you want to attach things or put 15mm plywood, with that you can mount whatever you want wherever you want without noggins.
 
nino nino said:
Do you have a link to that?
Is it new?

Last time I checked, BKR had nothing to say about the underlying board... You could/can have single gypsum board even

Fermacell is a good board, holds more than gypsum, but you should have noggings where you're going to attach things or put 15mm plywood; with that, you can mount whatever you want wherever you want without noggings
Since at least 2014 if I remember correctly...
Diagram showing three types of bathroom wall constructions: ceramic, plastic sheet, and painted surface with damp-proofing. Includes specifications like plywood thickness.
 
Unsure what kind of document it is. As far as I know, the "development" of the vptrumsväggen with the plywood was a project initiated by a number of insurance companies. It was supposed to be seen as an example of how to achieve the more abstract requirements found in the regulations. It is possible that it has been elevated to a rule by now, but I don't think so.
 
  • Like
Jonas Blom
  • Laddar…
Recommendation might be the right word, rule or requirement it is hardly. What the insurance companies can say about the matter is something else...
 
But as for the original question in the thread, I don't have a good answer. Other than it's not sufficient if you're going to install a sink or shower wall. It barely holds for a towel rack or toilet paper holder.
 
  • Like
Jonas Blom
  • Laddar…
Rickard.
Jonatan79 Jonatan79 said:
What the insurance companies can say about the matter is something else...
Insurance companies usually require that you follow industry regulations, so BBV in this case, and they don't require the wet room wall even though it's a really darn good universal solution that solves some problems more automatically than more budget solutions.

However, I think it sounds rather weak for a bathroom, and I would want to go in with more studs and plywood. I have an experienced carpenter/tiler at home, and they used max 45cc in the wall and max 30cc in the floor, and they took the reinforcement job very seriously.
 
  • Like
Jonas Blom
  • Laddar…
As I interpret fermacell's own documentation, it should be ok with a single board.
"
4.8.13 Use of fermacell
Fiber gypsum in wet rooms
n 12.5 mm fermacell Fiber gypsum c/c 600 mm
is approved and P-marked by SP-certification to be used in one layer in wet rooms. To meet the requirement for P-marking SC 0226-09 in wet rooms, all horizontal joints must have noggings."

page 40 in this description https://www.byggfaktadocu.se/monter...32/fil-files/monteringsanvisningfibergips.PDF
 
H hempularen said:
But when it comes to the original question in the thread, I don't have a good answer. Other than that it's not sufficient if you're going to install a sink or shower wall. It holds with doubt for a towel hook or toilet paper holder.
thanks puff of the original question.
 
Rickard. Rickard. said:
Insurance companies usually require that you follow industry standards, so BBV in this case, and they don't require the wet room wall even though it is a really damn good universal solution that solves some problems more automatically than more budget solutions.

However, I think it sounds quite weak for a bathroom and would want to go in with more studs and plywood. I have an experienced carpenter/tiler at home and they used max 45cc in the wall and max 30cc in the floor, and they took the reinforcement work very seriously.
thanks
The new wall will have cc30 with noggings.
The old walls, as mentioned, have masonite with cc60+ nogging.
On these walls, it sounds like I need to reinforce, either with plywood or open the wall and re-stud.
 
Considering that bathrooms were built with simple drywall and additional studs where needed near sinks, etc., and they are still built this way (though there are disclaimers regarding "säker vatten" and other recommendations), it works, but there's a reason why the wet room wall was developed.
 
The question is whether fermacell single board is suitable as a base for tiles if the studs are at cc60. Regular gypsum is not rigid enough. A wet room wall is not always tiled.
 
  • Like
Jonas Blom and 1 other
  • Laddar…
Jonatan79 Jonatan79 said:
Since at least 2014 if I remember correctly...
[image]
Where is that from?
As mentioned earlier, it's a recommendation, not a requirement (unless it has changed recently, in -14 it was not a requirement)
 
No requirement as mentioned.
 