Hi,
The floor in the living room was sagging. I have opened up the joists, and they are 70x195 cc50. I will later screw solid oak flooring 20mm directly onto the joists.
The span is 450cm, with the room being 700cm in length.
If I screw 1 piece of 45x195 on each side of the old joists, will that be enough? Or will the floor still sag even though it becomes 160x195mm?
Anyone with suggestions for solutions?
The floor in the living room was sagging. I have opened up the joists, and they are 70x195 cc50. I will later screw solid oak flooring 20mm directly onto the joists.
The span is 450cm, with the room being 700cm in length.
If I screw 1 piece of 45x195 on each side of the old joists, will that be enough? Or will the floor still sag even though it becomes 160x195mm?
Anyone with suggestions for solutions?
Unfortunately, nothing like that. The room below is the same size and will remain so. Otherwise, I could have built a wall below to support it.L Liteavvarje said:
After I wedged up against the walls, the floor still sagged a bit; it was 45X210 (Norwegian measurement). I attached a 45X195 on one side, using a lot of regular wood glue and fairly close spacing with thick screws. A must is to clamp the new piece in place by using several clamps to pull them together. What can be important is that if you just place and screw, you'll have a slight sag in the joists; I propped it up with beams about 5 mm from the basement floor before fastening them. It wasn't completely perfect, but it stopped creaking and rocking in an unfavorable way, there's probably a bit left, but it's manageable and nothing we directly notice.
Member
· Blekinge
· 10 117 posts
You need to increase to a beam width of 140 mm plus a screwed-and-glued 22 mm chipboard on top to reduce the deflection to a good level. You can achieve the width by screwing and gluing two 35x195 on either side of the old beam. Just two 45x195 are not enough. I assume that the old beams are of good wood quality. The new ones must be C24 or better.
Member
· Västra Götealand
· 156 posts
Krysskolva
Member
· Blekinge
· 10 117 posts
Cross-bracing reduces the deflection somewhat, but not sufficiently.
How do you calculate?J justusandersson said:You need to go up to a beam width of 140 mm plus a screwed-glued 22 mm chipboard on top to reduce the deflection to a good level. You can achieve the width by screwing and gluing 2 pieces of 35x195 on either side of the old beam. Just 2 pieces of 45x195 are not enough. I assume the old beams are of good timber quality. The new ones need to be C24 or better.
Yes, the old beams seem to be of good quality.
If I screw an extra 45x195 on one side then? So a total of 3 pieces of 45x195. They don't cost much. Yep, C24.
Member
· Blekinge
· 10 117 posts
What determines the deflection, apart from the wood quality, is the moment of inertia of the beams. This is a purely geometric concept calculated using the formula bxh^3/12. This means that a small increase in height has a greater effect than a small increase in width. You need to reach a total width of 190 mm to avoid adding extra height. It is screw gluing that is required to achieve full cooperation between the components involved.
Member
· Blekinge
· 10 117 posts
Cross bracing in combination with a screw-glued 22 mm flooring particle board would probably also work.