I am going to make a post that will need to support quite a lot of weight, say between one and two tons. The post is not the only support point, but it will take a large part of the weight from a roof.
I have some pieces of 2"6 k12 lumber that I plan to put together into a 6"6 post using a couple of wood screws. I thought that if you place two whole boards on the outside and leave several pieces with gaps in the middle layer, maybe the post will be more resistant to load that comes at a slight angle. Does anyone believe in this idea, or should I put together three whole boards?
 
Spacing does not increase strength.
It saves on timber without significantly reducing strength in one direction, but significantly reduces strength in the other.
Not recommended if you're looking to maximize load-bearing capacity.
 
thank you
 
Depending on how long the pole is, buckling rather than compression is the most critical factor, and then the construction of the column can make a big difference. The resistance to bending can change dramatically depending on the geometry of the pole.
 
A slightly thicker post is nicer too...instead of a toothpick ..;)
 
Gabbe1 said:
Depending on the length of the post, buckling and not pressure is the most critical, and how you construct your column can make a big difference.
The resistance to bending can change dramatically depending on the post's geometry.
However, it is the moment of inertia and the radius of gyration that are used to design columns. Although closely related to bending resistance, they are not entirely the same.
 
Mikael_L
Well, a 2"x2" should handle at least that weight, as a theoretical strength of spruce/pine. I’m not sure what safety margin a designer would apply.

But it's buckling that it can't withstand. So it's wise to join some beams together. And the resulting buckling resistance is better the larger the cross-section the post forms (with or without cavity).

I think you're good (although I don't know your unsupported buckling length!) with 2"x6" according to ...:
2 joined together to make a 4"x6"
3 joined together to make a 6"x6"
2 joined with a 2x3" between, so the profile looks like an H with an outer cross-section of 6x6"
4 joined, long side to short side, around the whole way so the resulting post becomes an 8x8" with a 4x4" hole in the middle.

In any case, keep in mind the moisture, e.g., 3 screwed together have the tendency to quickly draw in water capillarily in the gap, but then dry quite slowly.
 
Thanks for the tips.
It became 3x2"6
Felt very sturdy and since it is inside a sunroom, there won't be much moisture to be absorbed.
 