J justusandersson said:
Sure, but a bit later. Right now the dog is panting...
Hehe, same here, but the son:rofl:
 
HEA 260 corresponds in this context to 115x540 mm glulam. HEA 220 is closest to 115x450. Steel and glulam do not have completely parallel properties, so one must consider the context. The comparisons assume glulam in the highest strength class, L 40.
 
An HEA 260 of this length costs in the order of 8000 SEK. A glulam beam with the dimension 190x360 is less than half. The steel beam is also a bit more cumbersome to get in place and needs to be encased with plasterboard for fire protection reasons. These are some aspects to keep in mind.
 
J justusandersson said:
An HEA 260 of this length costs about 8000 SEK. A glulam beam with dimensions 190x360 is less than half. The steel beam is also a bit trickier to place and needs to be enclosed with gypsum for fire protection reasons. These are some aspects to keep in mind.
It only weighs around 300 kg or so :)

Single gypsum for decorative reasons, double for fire protection reasons. It's about designing for evacuation, not for the house to remain standing. If the load-bearing wall that is being taken down is stud-framed and single gypsum, that's the level you're looking at.
 
  • Wooden interior with visible staircase and door, featuring decorative gypsum walls.
It is not primarily the weight of the steel beam that is the problem, but rather its attachment to columns, etc.
 
I have received calculations from the designer now.
An IPE beam 220 with VKR 80 as columns is sufficient.
So now I'm just waiting for the construction company to get started.
 
I hope I'm not complicating things for you now. IPE 220 is approved but, in my opinion, gives a bit too much deflection for a primary beam (i.e., a beam that other beams rest on). I would suggest IPE 270 instead. Then, of course, the IPE profile provides a greater height than an HEA profile with the same capacity, but perhaps that's something you have discussed.
 
K
Don't you need to consider the load distribution and reinforce the foundation beam when making such a conversion? There can be quite significant forces if there are many people on the upper floor at the same time..
 
The VKR column must have an end plate that distributes the pressure over a larger area, but otherwise, there shouldn't be any major issues.
 
J justusandersson said:
The VKR pillar must have a concluding plate that distributes the pressure over a larger area, but otherwise there should be no major problems.
There are 8mm base plates in the drawing that I received from the designer.
 