I hope with my first post here on the forum to get an answer to a question I have...

A complete renovation of the upper floor in our 1920s villa is ongoing, and with this, new PEX pipes will be run from a centrally located shaft (by the chimney) "across the joists" out to the radiators at each gable.
I thus need to drill four 30mm holes in all the beams on one side to reach the gable, and two 30mm holes in all the beams in the other direction to reach the other gable.

The beams are 3"x8" on cc25" which corresponds to approximately 7x20cm on cc63cm.
The span of the beams between the outer wall and heart wall is about 4m.
  • On the side where 4 pipes will be run, and thus 4 holes per beam are necessary, the holes will be drilled roughly in the middle between the support against the outer wall and the heart wall.
  • On the side where 2 pipes will be run, and thus 2 holes per beam are necessary, the holes will be drilled about 1 meter from the support against the heart wall.
I assume I should drill in the middle of the beams' height?

The question is whether I need to be worried and contact a structural engineer to calculate, or if I should happily drill away?

Thankful for help :)
 
B BMannen said:
I hope with my first post here on the forum to get an answer to a question I have...

Total renovation of the upper floor is ongoing in our 1920s villa and with this, new PEX pipes will be drawn from a centrally located shaft (by the chimney) "across the joist" out to the radiators at each gable.
I thus need to drill 4 30mm holes in all beams on one side to reach the gable, and 2 30mm holes in all beams the other way to reach the other gable.

The beams are 3"x8" on cc25" which corresponds to approximately 7x20cm on cc63cm.
The span of the beams between the outer wall and the heart wall is about 4m.
  • On the side where 4 pipes are to be drawn and thus 4 holes per beam are necessary, the holes will be drilled approximately halfway between the support against the outer wall and the heart wall.
  • On the side where 2 pipes are to be drawn and thus 2 holes per beam are necessary, the holes will be drilled about 1 meter from the support against the heart wall.
I assume I'm drilling in the middle of the beams' height?

The question is whether I need to be worried and contact a constructor to calculate, or if I can happily drill away?

Thankful for help :)
You drill in the middle of the joist's height and as close to the middle of the span as possible, and there won't be any problems.
 
Mikael_L
No, you should probably avoid the middle of the span, as that's where the bending forces are greatest.

Feel free to drill the holes a bit closer to one of the supports.

If you're unsure, start by screw-gluing a piece of 12 or 18mm construction plywood on each side, say 1-2 meters long and as high as the beam (was it 20cm). Then drill the holes in the middle, this way the construction is still stronger than it was before.
 
Holes should be made where the shear forces are smallest, i.e., far from the supports, so closer to the middle of the span.

Otherwise, use plyfa as mentioned if you are unsure.
 
  • Like
seniorkonsult
  • Laddar…
Seems like we're talking about two midpoints?
Midway between the support points = worst.
Middle of the beam's (height) profile = best.
 
  • Like
fahlis and 1 other
  • Laddar…
Mikael_L Mikael_L said:
No, you should avoid the middle of the span, as that's where the bending forces are greatest.

Feel free to drill the holes a bit closer to one of the supports.

If you're unsure, start by screw-gluing a piece of 12 or 18mm construction plywood on each side, say 1-2 meters long and as high as the beam (was it 20cm). Then drill the holes in the middle, so this construction is still stronger than it was before.[/QUOTE
Stop!
In the middle, the shear forces are least! The greatest forces are at the supports!!
 
WRONG, completely wrong!
Imagine a long deck of cards, bend it and see where the cards shift the most!
 
  • Like
bossespecial
  • Laddar…
Midway up the beam's height, "best".
Mid-span between support points doesn't need to be the worst. The moment is managed with a couple of forces above and below the hole, the shear force is a bit "trickier" to handle, so it's advisable to avoid holes too close to the supports where the shear force is at its greatest.

What does the support of the roof look like? In my 1920s villa, the roof "rests" on the joist, which results in a somewhat different shear force distribution than for a standard beam.
 
Mikael_L
  • Like
BMannen
  • Laddar…
I would think that the wood guide is written for a slightly broader audience, which is why it's not that in-depth. Senior consultant shows an understanding of both power play and strength and I agree with him(y)

But it's as you write, plague or cholera, although one is easier to cure than the other:p
 
  • Like
Nahpets
  • Laddar…
Wow grateful for strong and quick response!
Have read a bit on the wood guide but since the exact calculation of what I need to do seems to require half a science, I'm thinking about the old carpenter's best tricks in tricky situations?

Over-dimensioning with 18mm k-plywood on each side of respective beam at 20x100cm and drilling centrally in height, in the middle of the span?
Would have wished it was just drilling, but the reinforcement is still feasible with minimal interventions in the floor... what do you think about that?
 
  • Like
seniorkonsult
  • Laddar…
Mikael_L Mikael_L said:
Not near the middle of the range according to this site.
[link]
Here we are talking about small holes and they should be placed in the 0-layer, i.e., midway through the beam height where the shear forces are minimal.
 