Handling 16m long glulam beams (roof beams)
Member
· Västernorrland
· 12 029 posts
Yes, I completely understand what you mean, but when discussing this, it sounds as if either the ground is giving way or that there is a significant overload over the parts of the beam that have no support? I'm thinking more like if the roof is calculated in the Swedish way with lots of snow and is really well-dimensioned, then the loads should reasonably be so evenly distributed that you practically don't get these movements you mention and thus wouldn't need a whole beam. I would understand the logic if each beam were on the verge of being too weak, if everything were a lightweight construction deluxe and you'd have to shovel the roof all winter. Then I understand the logic that everything is calculated and that a whole beam would of course be more rigid.G Gabbe1 said:
Self-builder
· Arvika
· 1 527 posts
Simplified, you have about 40kN/m, so with 50kPa on the ground, the footing will be about 800mm wide, which isn't particularly large.H HEA260 said:I have q_d = 32kN/m from the roof beam on the central support (wall_x). Then you add the weight for wall_x and the weight of the footing. I haven't had time to calculate more than an overview, asked for drawings for the existing foundation. I want to calculate the current load on the ground.
If I get the opportunity, I will follow the project and calculate the final footing after they start digging.
I'm also calculating the slab, you're probably right that it can be reduced to 100mm, 6s150.
Thank you for sharing your experience! It is very helpful!
Will the extension be done with a new foundation, or will you use an existing one since you mention an existing foundation?
New foundations.B bossespecial said:
Forgot to include the wind load. We also have a horizontal load of 10kN.
I'm aware of this, you assume correctlyG Gabbe1 said:I assume you are aware that there is more load on the middle support when using a continuous beam?
It's easy to think that with evenly distributed load on the beam, the loads are distributed on the supports according to: 1/4, 2/4, 1/4, which is also true if the beam is split at the middle support. But with a continuous beam, this is no longer the case.
It will matter for the dimensioning of the foundation. I have to compare the two cases. If I run with two beams instead of continuous, for example, it results in less ceiling height, something that is visibly different from the foundation. So I prefer to work with a continuous one in this case.
I also need access to a wheel loader. It feels like it will both cost (which a crane also does) and become more complicated.prototypen said:
The question of getting the beams up is to do it with a wheel loader with pallet forks if you can lay up the beams before the gable wall is built. Alt 2 is that a wheel loader can lay them just inside the gable wall and then you have to drag the beams afterwards.
Pouring 150 mm seems thick, more suitable for a tank garage.
Protte
I wrote 120mm slab, not 150mm
Self-builder
· Arvika
· 1 527 posts
I haven't looked at I-joist as an alternative (mostly because I haven't worked with it before). But I'll definitely check it out! Good idea if it works for the current span (9+6.2m).E erikjakan said:
I think it might be worth it, glulam is incredibly strong and attractive, but solid wood is expensive now as we all knowH HEA260 said:
Member
· Västerbottens län
· 18 051 posts
Having beams with measurements other than the "standard solution" is a hassle. It results in a lot of puzzling and more waste. Trust me, I've renovated with ceiling joists with CC varying around 750 mm. Protte