Okay, thanks! But if I go for 45x220, it won't be much more than it has been so far because it hasn't been visible to the eye at least, so I don't think it has been particularly much, otherwise I would have noticed.B bossespecial said:
And I meant that he might be able to keep the dimension he has by reducing the spacing between the studs. I understood it as he was satisfied with not increasing the dimension, not that he wanted to decrease it compared to what is there now.B BSOD said:
I can go up to 220x45 but was planning to make it wider compared to today, at least 4.5m but preferably up to 5m so then I can place them closer than cc600 because I want to avoid buying glulam.Nissens said:
If you use a sizing program, you quickly realize that even with cc 60, 225*45 is faaar from what is recommended.P ptlf said:
/Krille
Proper dimensioning is like a seatbelt - completely unnecessary until the "accident" happensP ptlf said:
/Krille
Do it like this.
Design according to Svenskt trä.
Calculate the total second moment of inertia for the construction, which is the number of beams multiplied by the second moment of inertia for one beam.
Then calculate the second moment of inertia for your section (beam) and ensure you reach the same total second moment of inertia as in Svenskt trä's design.
Search the internet for formulas for the second moment of inertia, and you should find them quickly. You can neglect the radius if your timber has such in the corners of its cross-section.
Design according to Svenskt trä.
Calculate the total second moment of inertia for the construction, which is the number of beams multiplied by the second moment of inertia for one beam.
Then calculate the second moment of inertia for your section (beam) and ensure you reach the same total second moment of inertia as in Svenskt trä's design.
Search the internet for formulas for the second moment of inertia, and you should find them quickly. You can neglect the radius if your timber has such in the corners of its cross-section.
If I'm not losing my way in the brain office now, the maximum deflection for a distributed load (snow) should have a double quadratic dependence on the beam's length, meaning there's a hell of a difference between a 3 and 5 m span.
I haven't dealt with this type of simple calculations for many years, so this is straight from memory.
I haven't dealt with this type of simple calculations for many years, so this is straight from memory.
That clarified everything... not...yoloboi said:If I'm not getting lost in my thinking now, the maximum deflection for a distributed load (snow) should have a double quadratic dependence on the beam's length, meaning there's a heck of a difference between a 3 and 5 m span.
I haven't dealt with these types of simple calculations for many years so this is freely from memory.
The reason your construction holds in practice but not in theory is because the dimensioning tool and dimensioning in general according to standards are based on taking into account safety factors and other partial coefficients to account for various types of uncertainties. This may involve uncertainties regarding material quality, load-bearing capacity with regard to a myriad of factors such as moisture and load duration, the load in question, etc.
Things can go really wrong if you remove all these margins. One day it might be unfortunate that the structure has suffered moisture damage and there is a significant snowfall. That said, 45x220 holds for 5 m and c/c 600 as well as for snow zone 2 in the ultimate limit state according to all the rules except for deflection. There you get 20 mm deflection in the middle, which is considered a bit high compared to recommendations if you, for example, compare with L/300 ~ 17 mm. But in this case, I have, as mentioned, included quite a lot of safety margin, so 45x220 will likely hold for 5 m.
Things can go really wrong if you remove all these margins. One day it might be unfortunate that the structure has suffered moisture damage and there is a significant snowfall. That said, 45x220 holds for 5 m and c/c 600 as well as for snow zone 2 in the ultimate limit state according to all the rules except for deflection. There you get 20 mm deflection in the middle, which is considered a bit high compared to recommendations if you, for example, compare with L/300 ~ 17 mm. But in this case, I have, as mentioned, included quite a lot of safety margin, so 45x220 will likely hold for 5 m.
Thanks for the good information! Moisture damage can probably be avoided if you make sure the roof is tight, and you don't need to use the beams with the worst knots, and the amount of snow is something we're used to keeping track of up here, so good with your input.S scorp1on said:The reason your construction holds in practice but not in theory is because the sizing tool and sizing in general according to standards are based on considering safety factors and other partial coefficients to account for various types of uncertainties. It can involve uncertainties about the quality of the material, load-bearing capacity with regard to a variety of factors such as moisture and load duration, the load in question, etc.
It can go really badly if you remove all these margins. One day it might be unfortunate that the structure has suffered moisture damage and there comes plenty of snow. With that said, 45x220 holds for 5 m and c/c 600 as well as for snow zone 2 in ultimate limit state according to the rules except for the deflection. There, it gets 20 mm deflection in the middle, which is considered a bit higher compared to recommendations if, for example, you compare with L/300 ~ 17 mm. But in this case, as I said, I've added a lot of safety margins, so 45x220 should hold for 5 m.