P ptlf said:
Thanks! It was something like that I wanted to know because that where they bend down in the middle without any load other than their own weight if I understood it correctly?
No, it only shows how many times greater the deflection becomes compared to today.
 
B bossespecial said:
No, it only shows how many times larger the deflection becomes compared to today.
Okay, thanks! But if I go for 45x220, it won't be much more than it has been so far because it hasn't been visible to the eye at least, so I don't think it has been particularly much, otherwise I would have noticed.
 
B
Nissens Nissens said:
I wrote nothing about reducing the dimension.
No, but the original poster wants to use weaker trusses than recommended. And you suggested tighter spacing...
 
Nissens
B BSOD said:
No, but the original poster wants to use weaker rafters than recommended. And you suggested closer spacing...
And I meant that he might be able to keep the dimension he has by reducing the spacing between the studs. I understood it as he was satisfied with not increasing the dimension, not that he wanted to decrease it compared to what is there now.
 
  • Like
fribygg
  • Laddar…
Nissens Nissens said:
And I meant that he might be able to maintain the dimension he has by reducing the cc between the studs. I understood it as he was satisfied with not increasing the dimension, not that he wanted to reduce it compared to what is there now.
I can go up to 220x45 but was planning to make it wider compared to today, at least 4.5m but preferably up to 5m so then I can place them closer than cc600 because I want to avoid buying glulam.
 
  • Like
Nissens
  • Laddar…
K
P ptlf said:
I can go up to 220x45 but was thinking of making it wider compared to today, at least 4.5m but preferably up to 5m so then I can set closer than cc600 to avoid buying laminated timber
If you use a sizing program, you quickly realize that even with cc 60, 225*45 is faaar from what is recommended.

/Krille
 
K Krille4 said:
If you use dimensioning software, you quickly realize that even with cc 60, 225*45 is faaaar from what is recommended.

/Krille
I know that, but what I have now should have been at the dump a long time ago according to the dimensioning software too....
 
K
P ptlf said:
I know that, but what I have now should have been on the ground long ago according to the dimensioning program as well....
Proper dimensioning is like a seatbelt - completely unnecessary until the "accident" happens ;) Personally, I would never dare to dimension so lightly in Västerbotten to save "a few" thousand kronor. I was glad about that last winter when we were abroad for three weeks while it snowed a lot and drifted up almost 2 meters of snow on one side of the carport roof.

/Krille
 
  • Like
ptlf
  • Laddar…
P
Do it like this.

Design according to Svenskt trä.

Calculate the total second moment of inertia for the construction, which is the number of beams multiplied by the second moment of inertia for one beam.

Then calculate the second moment of inertia for your section (beam) and ensure you reach the same total second moment of inertia as in Svenskt trä's design.

Search the internet for formulas for the second moment of inertia, and you should find them quickly. You can neglect the radius if your timber has such in the corners of its cross-section.
 
P
If I'm not losing my way in the brain office now, the maximum deflection for a distributed load (snow) should have a double quadratic dependence on the beam's length, meaning there's a hell of a difference between a 3 and 5 m span.

I haven't dealt with this type of simple calculations for many years, so this is straight from memory.
 
Nissens
yoloboi said:
If I'm not getting lost in my thinking now, the maximum deflection for a distributed load (snow) should have a double quadratic dependence on the beam's length, meaning there's a heck of a difference between a 3 and 5 m span.

I haven't dealt with these types of simple calculations for many years so this is freely from memory.
That clarified everything... not...
 
  • Like
ptlf
  • Laddar…
P
Nissens Nissens said:
That clarified everything... not...
Deflection = constant * length^4

Anyone who wants to understand better needs to study beam deflection. Anyone who wants to design seriously needs to understand the applicable standards.

:)
 
  • Like
ptlf
  • Laddar…
S
The reason your construction holds in practice but not in theory is because the dimensioning tool and dimensioning in general according to standards are based on taking into account safety factors and other partial coefficients to account for various types of uncertainties. This may involve uncertainties regarding material quality, load-bearing capacity with regard to a myriad of factors such as moisture and load duration, the load in question, etc.

Things can go really wrong if you remove all these margins. One day it might be unfortunate that the structure has suffered moisture damage and there is a significant snowfall. That said, 45x220 holds for 5 m and c/c 600 as well as for snow zone 2 in the ultimate limit state according to all the rules except for deflection. There you get 20 mm deflection in the middle, which is considered a bit high compared to recommendations if you, for example, compare with L/300 ~ 17 mm. But in this case, I have, as mentioned, included quite a lot of safety margin, so 45x220 will likely hold for 5 m.
 
S scorp1on said:
The reason your construction holds in practice but not in theory is because the sizing tool and sizing in general according to standards are based on considering safety factors and other partial coefficients to account for various types of uncertainties. It can involve uncertainties about the quality of the material, load-bearing capacity with regard to a variety of factors such as moisture and load duration, the load in question, etc.

It can go really badly if you remove all these margins. One day it might be unfortunate that the structure has suffered moisture damage and there comes plenty of snow. With that said, 45x220 holds for 5 m and c/c 600 as well as for snow zone 2 in ultimate limit state according to the rules except for the deflection. There, it gets 20 mm deflection in the middle, which is considered a bit higher compared to recommendations if, for example, you compare with L/300 ~ 17 mm. But in this case, as I said, I've added a lot of safety margins, so 45x220 should hold for 5 m.
Thanks for the good information! Moisture damage can probably be avoided if you make sure the roof is tight, and you don't need to use the beams with the worst knots, and the amount of snow is something we're used to keeping track of up here, so good with your input.
 
S
Note that I counted with snow zone 2.
 