If I have a garage wall 3m from the house and need to build fire-rated, will this material suffice: (is it EI30 the insurance company requires? When I talked to my company, they only said it's built according to building codes...)

- Sheet metal vp20 exterior
- Wooden battens
- Windproofing membrane
- 145 standing wooden studs, glass wool 145
- Durable plastic
- 45 horizontal wooden studs, glass wool 45
- Plywood
- Gypsum board
- Sheet metal vp20 interior

Do I need to add anything?
 
Rickard.
I think you misunderstood a bit but ei30 always meets that wall so maybe it doesn't matter ;)
 
The minimum requirement for EI30 is a 95 mm insulated wall with plasterboard on both sides, so your construction, as far as I understand, is significantly better than that.
 
Rickard.
M mlkjhr said:
The minimum requirement for EI30 is presumably a 95 mm insulated wall with gypsum on both sides, so your construction is, as far as I understand, significantly better than that.
The minimum is actually a 45mm stud without insulation with at least 12.5mm gypsum on each side.

With your example, you can go down to 12mm plywood instead of gypsum, but this is not directly transferable to a wall that only has a board on one side. However, the OP's example is so far from the limit that it becomes irrelevant to calculate.

Source träguiden.se
 
Ah, nice, I've been in contact with the fire protection association, which sent me to Isover, which sent me to Kami, which sent me to WSP, which sent me to Gyproc's handbook... No one wants to take responsibility ☺️ So it'll just be plyfa under the inner sheet so I have something to attach any shelves and such to. Thanks for the response.
 