Planning to put together two pressure-treated beams 45x145 so it becomes 90x145. Joist hanger against wooden wall on one side and resting on a 90-post 5 meters away. It should work without additional posts/support along the way, right?
Pidde
Pidde
Moderator
· Stockholm
· 57 861 posts
Well, it depends on what you need to add, if it has to bear more than its own weight, it's probably too weak. It probably won't break if you have ONE person jumping on it, but it will likely bend quite a bit.
If you're thinking of using it to support a deck, I would guess you'll need a glulam beam that is at least 300 in height. But someone would need to calculate that. There are dimensioning programs online.
If you're thinking of using it to support a deck, I would guess you'll need a glulam beam that is at least 300 in height. But someone would need to calculate that. There are dimensioning programs online.
Best answer
https://www.byggahus.se/forum/threads/hur-stor-blir-nedboejningen.297641/#post-2740684
Here is a calculation for a similar load case, albeit with a span of 4-4.5 m but with a load of 100 kg in the middle. Berniberg claims that the deflection would only be 1.9 mm.
I calculated the load case in sagulator (as if the joists were a shelf with 1 kg load) and found that the deflection would be negligible (0.6 mm).
That said, I believe (here I'm guessing) that with the influence of moisture, consider precipitation, there will be a deflection over time that will become more or less visible. If you can increase the dimension in height, it is better.
Disclaimer: I only link to previous calculations and to a calculation site called sagulator. I have not calculated it myself. Wood structures are tricky but more information can be found at https://www.traguiden.se/konstruktion/dimensionering/dimensioneringsvarden-och-barformaga/
Here is a calculation for a similar load case, albeit with a span of 4-4.5 m but with a load of 100 kg in the middle. Berniberg claims that the deflection would only be 1.9 mm.
I calculated the load case in sagulator (as if the joists were a shelf with 1 kg load) and found that the deflection would be negligible (0.6 mm).
That said, I believe (here I'm guessing) that with the influence of moisture, consider precipitation, there will be a deflection over time that will become more or less visible. If you can increase the dimension in height, it is better.
Disclaimer: I only link to previous calculations and to a calculation site called sagulator. I have not calculated it myself. Wood structures are tricky but more information can be found at https://www.traguiden.se/konstruktion/dimensionering/dimensioneringsvarden-och-barformaga/
Thanks!-RB- said:
[link]
Here is a calculation for a similar load case, admittedly with a span of 4-4.5 m but with a load of 100 kg in the middle. Berniberg claims there that the deflection would only be 1.9 mm.
I calculated the load case in the sagulator (as if the beams were a shelf with a 1 kg load) and found the deflection to be negligible (0.6 mm).
That being said, I believe (taking a guess here) that with the influence of moisture, think precipitation, there will be deflection over time that will become more or less visible. If you can increase the dimension in height, it is better.
Disclaimer: I am only linking to previous calculations and a calculation page called sagulator. I have not done the calculations myself. Wood structures are tricky but more information can be found at [link]
Member
· Blekinge
· 10 117 posts
If the beam only needs to support its own weight, there is no advantage to using two studs. However, it might look better. The instantaneous deflection should be about 2 mm, but it will increase over time since it is exposed outdoors; however, it will not be greater than acceptable.