We are planning to extend what has been a walkway on the upper floor. It is supported by a 42 x 315 glulam beam, which according to the construction drawing should be replaced with a 90 x 315. Now that we have spoken with the carpenter, he thinks it should be possible to reinforce the existing one by gluing and screwing on an identical one. Is it OK to do so?

Then I'm wondering in that case, which dimension? 42 x 315 no longer seems to be available as standard and neither does 56 x 315. Would 66 x 315 then be applicable?
 
  • Technical drawing of a construction plan detailing the replacement of a 42x315 beam with a 90x315 beam in an upper floor corridor.
  • Construction drawing showing the replacement of a 42x315 beam with a new 90x315 one for an upper floor air passage expansion.
  • Construction plan detail showing a beam replacement from 42x315 to 90x315, related to a balcony structure on an upper floor.
42, 56, 66 and 78 mm wide laminated beams are produced by splitting. They are mostly stocked in smaller heights. However, all sizes are usually available as special order items. If you glue a 56x315, the result is comparable to 90x315. 2 pieces of 42x315 are not enough to meet the architect's requirements.
 