In our basement/lower floor, we have an I-beam as extra support for the cast intermediate floor. It rests partly on masonry partition walls and partly on timber posts that we want to replace because we want to remove all organic material. My idea is to replace the timber posts with 120*190*590 lecablocks stacked on top of each other. Will this hold?
There are 4 posts that need to be replaced. They are about 2 meters apart.

Brick wall and wooden support beam in a basement, with construction debris on the concrete floor, illustrating a renovation project to replace wooden posts.
 
It is a somewhat peculiar construction. First, you should get an idea of the loads the beam handles and what type of beam it is (profile and dimension), at least if you want a more analytical approach. Drawings are the best basis.
 
  • Like
andost
  • Laddar…
J justusandersson said:
It is a bit of a strange construction. First, one should get an idea of the loads the beam is supporting and what type of beam it is (profile and dimension), at least if one wants a more analytical approach. Drawings are the best basis.
Mm. Unfortunately, there are no drawings. Or yes, there are, but they don't match. According to the information, the intermediate floor was supposed to be wood, but it was changed. So it's a bit difficult... I could start by measuring the thickness of the floor and the dimensions between the load-bearing walls to be able to calculate the load... ?
 
A andost said:
I could start by measuring the thickness of the floor structure and the dimensions between the load-bearing walls to be able to calculate the load... ?
An excellent idea. Plus check the beam's profile in mm.
 
  • Like
andost
  • Laddar…
The floor slab is 160mm
The I-beam is 120 wide and 125 high.
The beam sits by the wall marked in red in the image below. The wall is framed (single brick)

The span between the outer wall and the beam is 300cm on one side and 400 on the other side.

Floor plan with rooms labeled and red lines marking the position of an I-beam near a wall. The beam spans between outer wall and marked wall.
 
Last edited:
The beam measurements do not match any profile known to me. Have you really measured correctly? I think it seems proportionally higher than it is wide.
 
J justusandersson said:
The beam dimensions do not match any profile known to me. Have you really measured correctly? I think it seems proportionally taller than it is wide.
Could it be a HEB 120? It is 120*120...

https://brommastal.se/stal-2/heb-balk/
 
Then the thickness of the lower flange should be 11 mm.
 
Wouldn't it be easier to replace the studs with standing square steel profiles with the same width as the beam? Standing on iron plates with felt or rubber sheeting against the concrete.
 
  • Like
Fadai
  • Laddar…
J justusandersson said:
Then the thickness of the lower flange should be 11 mm.
Will bring a caliper next time :thinking:
 
Steel is certainly an interesting option as support, but first, one must know what loads are involved.
 
  • Like
Fadai
  • Laddar…
J justusandersson said:
Then the thickness of the lower flange should be 11 mm.
Correct

Ruler measuring rusty metal surface in dim light.
 
A HEB 120 is quite a strong beam. With a span of 4 meters, it can handle a distributed load of 6 kN per meter. Can you specify exactly where the beam is located and how long it is?
 
J justusandersson said:
An HEB 120 is quite a strong beam. With a span of 4 meters, it can support a distributed load of 6 kN per meter. Can you specify exactly where the beam is located and how long it is?
Yep. See below.
Then we have a brick wall right next to the beam, so the beam doesn't take the entire load.

The ground floor looks like this:
Floor plan showing ground floor layout with rooms labeled samvarorum, duschrum, arbetrum, gästrum, and hobbyrum. Blue measurements indicate dimensions.

The upper floor:

Floor plan sketch showing measurements and labeled rooms, including living room, bedrooms, kitchen, and dining area, with dimensions marked in red and blue.
 
  • Floor plan showing ground floor layout with rooms labeled, including living room, bathroom, hobby room, and office. Blue lines highlight beams and load distribution.
The standing posts that are to be replaced (the I-beam is not to be replaced) are 120x120, so perhaps the question is really what the compressive strength is for such a post. The I-beam has support with approximately 2 meters intervals – either a post or a masonry wall.
 