Reinforce wooden joists Bathroom...
Homeowner
· Västragötaland
· 348 posts
Hello, I want to double-check with the rest of you how. I'm thinking. I'm renovating the house and converting a former bedroom into a bathroom.
As it seems, I have to deviate from the recommendations (GVK).
___________________________________
My basic conditions are:
- Existing floor joist C24 45x190 CC60 Support distance 2990mm
- Floor chipboard 22mm
On this, I plan to glue/screw floor gypsum, then reinforce and apply leveling compound/floor screed.
___________________________________
As it looks, the problem is that the floor joist is 190mm instead of the recommended 220mm.
What do the rest of you think, with the double reinforcement regarding floor gypsum + reinforcement/floor screed? Will the floor achieve the equivalent stability that the GVK recommendations seek?
The alternative is that I rip up the entire floor and add additional joists on cc30, followed by the aforementioned Floor chipboard/floor gypsum/reinforcement and floor screed.
Grateful for your objections and thoughts.
/Tobias
As it seems, I have to deviate from the recommendations (GVK).
___________________________________
My basic conditions are:
- Existing floor joist C24 45x190 CC60 Support distance 2990mm
- Floor chipboard 22mm
On this, I plan to glue/screw floor gypsum, then reinforce and apply leveling compound/floor screed.
___________________________________
As it looks, the problem is that the floor joist is 190mm instead of the recommended 220mm.
What do the rest of you think, with the double reinforcement regarding floor gypsum + reinforcement/floor screed? Will the floor achieve the equivalent stability that the GVK recommendations seek?
The alternative is that I rip up the entire floor and add additional joists on cc30, followed by the aforementioned Floor chipboard/floor gypsum/reinforcement and floor screed.
Grateful for your objections and thoughts.
/Tobias
Member
· Blekinge
· 10 117 posts
Your 45x190 in combination with screwed-glued 22 mm chipboard is sufficient to meet both deflection and flex requirements. Mainly due to the limited span. The other adds nothing from a stability perspective.
Homeowner
· Västragötaland
· 348 posts
Thank you for your response. What is your reasoning based on, can I calculate this in some way? As it is. Now there is a 30mm difference in the joists compared to the recommendations, which should then imply a certain/significant difference due to the deviation.J justusandersson said: