S SueCia said:
There is some missing information in the central register, such as rated current and area, but it's not a disaster. I still think it looks decent. I don't understand the thing with so many residual current circuit breakers, but that's a matter of taste and not directly wrong.

Placing the residual current device to the right on the middle row even though according to the documentation it protects the entire middle row and bottom row is a bit strange, but not wrong.

The most serious thing we can see from the pictures is definitely the non-insulated conductors outside the central and the large cutout in the casing.
Residual current circuit breakers are very good for sockets and fixtures outdoors.
If they trip, the indoor installation is not affected, e.g. the freezer or the power supply to the burglar alarm...
 
  • Like
Roger Fundin
  • Laddar…
S
P Peter787 said:
Residual current devices are very good for outlets and fixtures outdoors.
If they trip, the indoor installation is not affected, e.g. the freezer or the power supply to the burglar alarm...
I know, but it's not relevant in this case as TS has received several residual current devices that are, in my opinion, completely unnecessary, and none of them pertain to outdoor electricity...

I prefer one residual current device for all indoor electricity and one for all outdoor electricity.
Why would it be negative for the burglar alarm to be on the same residual current device as the outdoor electricity? That was a bad example, I can even see advantages to having the burglar alarm on the residual current device for outdoor electricity :)
 
S SueCia said:
can even see the advantages of having the burglar alarm on the ground fault circuit interrupter for the outdoor electricity
Well. Nowadays, most alarms probably have a battery backup. But I think it was in the early '90s that it was known (or maybe it was an urban legend) that Volvo had the car alarm on the same fuse as the indicators. It was apparently easy to pry off one of the indicator lenses and short circuit to the body. So many Volvo cars that were burgled also had a broken indicator. The alarm initiates flashing when it goes off, and the fuse blows immediately.

You don't want a thief to be able to neutralize the house alarm by causing a ground fault in a garden lamp.
 
Last edited:
  • Like
kashieda and 3 others
  • Laddar…
T Thomas_Blekinge said:
Find five errors!
No, that's not correct. The wires must not hang freely accessible.
He should have installed a panel that's wider and covers the hole in the nice wallpaper. Don't pay!
Are you sincere?? Electrical company? Friend?
 
P
S SueCia said:
I know, but it's not relevant in this case as the OP has received multiple personal protection breakers which, in my opinion, are completely unnecessary. And none of them pertain to the outdoor electricity...

Then I prefer a residual current circuit breaker for all the indoor electricity and one for all the outdoor electricity.
Why would it be negative for the burglar alarm to be on the same residual current circuit breaker as the outdoor electricity? That was a bad example, I can even see advantages of having the burglar alarm on the residual current circuit breaker for the outdoor electricity :)
A cunning burglar would certainly appreciate your stance, causing a ground fault at the outlet outside and the alarm is dead within a few days when a possible backup battery is drained.
 
S SueCia said:
I prefer a residual-current device (RCD) for all indoor electricity and an RCD for all outdoor electricity.
Why would it be negative for the burglar alarm to be on the same RCD as the outdoor electricity? That was a bad example, I can even see advantages to having the burglar alarm on the RCD for outdoor electricity.
I would suggest at least two RCDs for indoor electricity, where lighting and outlets are reasonably evenly distributed among these and where each (main) part of the residence has at least one light point per RCD.

No, never any significant part of the burglar/fire alarm on the outdoor electricity's RCD.
It's better for the alarm to be on the same RCD as the heating, because then you at least get a notification if the heating might be without power.

Admittedly, it's just as easy to open the meter cabinet and turn off the main switch as it is to create a ground fault.
 
  • Like
Roger Fundin and 1 other
  • Laddar…
S
P Peter787 said:
A cunning burglar will surely appreciate your approach, cause a ground fault on the outlet outside and the alarm is dead within a few days when a possible backup battery is depleted.
Why would one even have a burglar alarm if they plan to ignore it when it goes off?
 
  • Like
Müssli
  • Laddar…
S
Demmpa Demmpa said:
I would say at least two RCDs for the indoor electricity, with lighting and sockets fairly evenly distributed across these, and that each (main) part of the residence has at least one light point per RCD.

Never have any essential part of the burglary/fire alarm on the outdoor electricity's RCD.
It's better for the alarm to be on the same RCD as the heating, so you at least get a notification if the heating might be without power.

Admittedly, it's just as easy to open the meter cabinet and turn off the main switch as it is to create an earth fault.
As I said, I see advantages to having the alarm on the outdoor electricity, just as I see advantages to having it on the indoor electricity.

From a burglary protection standpoint, it's definitely best to have it on the outdoor electricity.
 
  • Like
Müssli
  • Laddar…
P
S SueCia said:
As I said, I see advantages in having the alarm on the outdoor unit, just as I see advantages in having it on the indoor unit.

From a burglary protection point of view, it's guaranteed best to have it on the outdoor unit.
I've worked for 12 years at Securitas and led installations of, among other things, burglar alarms, but you know best...
 
  • Like
kashieda
  • Laddar…
S
P Peter787 said:
I have worked for 12 years at Securitas and led installations of, among other things, burglar alarms, but you know best...
16 years here, what are you trying to say?
 
  • Haha
  • Like
Dilato and 1 other
  • Laddar…
jakobsbygge
are you allowed to leave it like in the picture?
 
  • Close-up of an electrical panel with circuit breakers, some with visible copper wires, red numbers, and a red circle highlighting specific components.
  • Haha
Jonas Arvidsson
  • Laddar…
S
jakobsbygge jakobsbygge said:
is it okay to leave it as shown in the picture?
Yes, no problem with that.
 
  • Like
Dilato
  • Laddar…
P
S SueCia said:
16 years here, what do you want to say?
Hopefully not with alarm installations, we hope.
 
S SueCia said:
As I said, I see advantages in having the alarm on the outdoor electricity, just as I see advantages in having it on the indoor electricity.

From a burglary protection standpoint, it is definitely best to have it on the outdoor electricity.
What are the advantages?

Why is it an advantage from a burglary protection standpoint to have the burglar alarm on the outdoor electricity?
 
G GoGetLost said:
The charging station should have its own RCD if I remember correctly.
No, but the requirement is that a charging station must have its own fuse, either in the box or at the feed. So it can share a residual-current device with others, even if it might be unwise.
 