Renovation project showing a widened door opening in a room, with construction materials on the floor and visible tools. Building permit document showing non-load-bearing wall information: 2"x3" studs, gypsum boards. Includes insulation details and beam sizes. Image of a building plan document detailing roof construction, mentioning 2" x 7" wooden beams, related to a discussion on renovating a non-load-bearing wall. Floor plan of a 1973 single-story house with a circled area indicating a widened door opening between a bedroom and another room. Blueprint of a two-story house section with height measurements 2.5m and 2.4m indicated, illustrating floor levels and structural design.

I'm renovating a bedroom and have made a doorway twice as wide. 80->160 cm.

I have a split-level house with a flat roof built in 1973. According to the building permit documents, the wall I've worked on is not load-bearing since the framework is 2x3 inches.

Should I relieve with a disturbing beam or should I trust the building permit documents?
 
Since the width of the house is about 7 meters and the roof is supported by 2x8 inch joists (50x200 mm), the marked wall must be load-bearing. There is also no beam in the ceiling above the wall. If the opening is not to be wider than you have already made it, it is easy to install a beam over the actual opening. The fact that it hasn't collapsed yet is because there is no snow at the moment.
 