Is the electrical box located on the outside?
 
useless useless said:
Is the power socket on the outside?
no, it's in an exterior wall.
 
Jschoenf87 Jschoenf87 said:
yes, it's not optimal but the electrician said it was ok if properly sealed around the box, which was apparently not done
I think you misunderstand, the problem is the air in the flex conduits that then gets cooled and can condense and then run down to the box. If out can cause a short circuit.

It can be prevented by sealing the pipe at one end with insulation or similar, but it feels like an unnecessary solution since you can instead place the conduits on the warm side of the insulation and avoid the problem altogether.
 
Jschoenf87 Jschoenf87 said:
no, it's in an exterior wall.
Yes, I was fooled by all the plastic in the last picture. I assume there's not plastic on both sides of the wall...
 
C Cerb said:
I think you misunderstand, the problem is the air in the flex tubes that gets cooled down and can condense, then run down to the box. It could cause a short circuit.

You can prevent air migration by sealing the pipe at one end with insulation or similar, but it seems like an unnecessary solution since you can instead place the tubes on the warm side of the insulation and avoid the problem entirely.
ok! when we open the wall, I'll make sure the pipes are sealed
 
useless useless said:
Yes, it was me who was fooled by all the plastic in the last picture. I assume there's no plastic on both sides of the wall...
no, on the inside it's ångspätt, then insulation and wind barrier
 
Jschoenf87 Jschoenf87 said:
ok! när vi öppnar väggen ska jag se till att det blir tätat i rören
No, place them instead on the warm side of the insulation.
 
Jschoenf87 Jschoenf87 said:
ok! when we open the wall, I'll make sure the pipes are sealed
You don't need to open the wall to seal the pipes. It's enough to open the junction box.
 