I recently conducted a thermography on an extended room which showed lots of "infiltrations" of cold air. My conclusion is that the vapor barrier was not properly sealed with tape or similar. I wonder if anyone has suggestions on the best way to fix this? The walls have OSB+gypsum and behind that is the foil, probably we need to open them as the first step. All inputs are welcome.
 
What does the picture look like?
 
A
Jschoenf87 Jschoenf87 said:
Hello!

I recently conducted a thermographic assessment on an extension room that showed lots of "infiltrations" of cold air. My conclusion is that the vapor barrier wasn't sealed properly with tape or similar materials. I'm wondering if anyone has suggestions on the best way to repair this? The walls have OSB + plasterboard, and behind that, there's the foil. Most likely, we'll need to open them as the first step. All inputs are welcome.
If you have the vapor barrier directly behind the OSB board, you can't avoid holes in it.

The only way to avoid holes is to have an installation rule as a buffer.
That means the vapor barrier is mounted directly on the frame, and on the outside, you mount a 45x45 or 28x70, then OSB and plasterboard.
 
I am completely onboard with the smaller screw holes etc. I can consider those negligible but definitely not optimal.
 
Jonatan79 Jonatan79 said:
What does the picture look like?
sending 2 examples
Thermal and regular images of a ceiling, showing temperature variations.

Thermal image of a room corner showing temperature variation and a standard visual image of the same corner with visible flooring and a sofa.
 
Any leaks in the vapor barrier do not affect the insulation's insulating ability. If it looks like that, insulation is missing, not the vapor barrier.
 
  • Like
Edlunn and 3 others
  • Laddar…
My thought too, but I know too little about thermal cameras.
Looks like thermal bridges/poor insulation.

Is it drafty, or are you checking thermographically out of curiosity?

How does your house look otherwise?
 
The entire test is conducted by creating a vacuum in the house, extracting all the air from it, which causes cold air to be drawn in if there are leaks. Then, all areas are inspected with a thermal camera.

Interesting with the insulation aspect. It would make things easier.
 
Jschoenf87 Jschoenf87 said:
The entire test is conducted by creating an underpressure in the house, extracting all the air from the house which means if there are leaks, cold air will be drawn in. Then a thermal camera is used to check all the places.

Interesting with the insulation aspect. That would simplify things a bit.
But what kind of supply air is there in the extension?
What does the ventilation look like otherwise?

Finally, the air must come from somewhere.
 
Dr Benz Dr Benz said:
But what kind of incoming air is in the extension?
What does the ventilation look like overall?

Eventually, air has to come from somewhere.
there is a 10cm air supply installed. The house has a mechanical exhaust system, it works fine.

and yes, you can feel some cold drafts + the room doesn't warm up properly even though the heat is on max.
 
Jschoenf87 Jschoenf87 said:
there is a 10cm supply air device installed. The house has a mechanical exhaust system, it works fine.
Ok. It looks like underfloor heating. And it also looks like the loop doesn't extend all the way to the interior wall? And also a window in the same area. Could that be enough to create what's shown in the picture?

If it is so poorly sealed, you should be able to max out the ventilation and hold a candle where it looks cold. One should be able to see flickering there if that's the case?

Otherwise, I'm thinking outer wall and thermal bridge insufficient insulation.

Do you have pictures from the actual construction?

Is it drafty in the room or is it just something discovered by chance?
 
  • Like
Freniño and 1 other
  • Laddar…
Dr Benz Dr Benz said:
Ok. It looks like underfloor heating. And it also looks like the coil does not go all the way out to the inner wall? And additionally a window in the same area. That may be enough to get it as in the picture?

If it is so poorly sealed you should be able to max out the ventilation and hold a light where it looks cold. I think you should be able to see flickering there if so?

Otherwise, I'm thinking exterior wall and thermal bridge with inadequate insulation.

Do you have pictures from the actual construction?

Is it drafty in the room or is it just something discovered by chance?
It started when I felt a draft in the pocket frame of the sliding door that sits between the existing house and the extension. It wasn't sealed at all with tape/soft seal and wood, there was just a piece of wood. A lot of cold air was blowing in there. This has been improved now, but there are other places left as you can see.
Here's a picture from one corner of the room before insulation in the wall
Wooden wall framework with rods and gaps before insulation, located in a corner room of a house under construction. Wiring box visible.

connection to the house (the electric box must be 100% better sealed)

A room corner with a partially installed vapor barrier, exposed insulation, electrical wiring, and a section of an unfinished wooden frame wall.
 
Jschoenf87 Jschoenf87 said:
It started with me feeling a draft in the pocket frame of the sliding door that is between the existing house and the extension. It was not sealed at all with tape/sealant and stud connection, there was just a stud. A lot of cold air was blowing in. This has been improved now, but there are other places left as you can see.
Here's a picture from one corner of the room before insulation in the wall
[image]

connection to the house (the electrical box must be sealed 100% better)

[image]
Yes. But then you have a reason that it is not sealed. Unfortunately, I can't give you tips on how to fix it other than the obvious answer...

It's just so frustrating that when something is done, it's not done properly...
 
  • Like
Joak
  • Laddar…
Jschoenf87 Jschoenf87 said:
connection to the house (the junction box must be sealed better 100%)

[image]
Then the hoses should also be on the warm side of the wall to avoid condensation.
 
C Cerb said:
Then the hoses should also be on the warm side of the wall to avoid condensation.
yes, it's not optimal but the electrician said it's okay if you properly seal around the box. which obviously wasn't done
 