Hi, we are building a bathroom on the upper floor of our house from 1930. One of the beams, where we need to run the drain, has several notches from earlier modifications (see picture).

The dimensions are about 80x220-230, it's planed in some places which causes the difference. Free length is 4 meters.

How can we reinforce this to make it possible to create a new hole, is it even possible? Unfortunately, we cannot use the previous holes as they aren't deep enough all the way, and there is a metal reinforcement on the backside.
 
  • Diagram showing a wooden beam with multiple notches and dimensions labeled, including a free length of 4 meters, intended for a bathroom renovation project.
  • Wooden beam with multiple notches in a 1930s house bathroom renovation, showing areas where previous holes have been made.
P
You can drill the holes more in the middle of the joist if they are 50-120mm holes, then you can glue-screw on construction plywood that is cut to 220x1200mm and centered over the holes.

It looks like there is a wide gap between the joists? The aim is for cc300-400mm in the joist spacing in bathrooms if you plan to have ceramic flooring.
 
  • Like
Tompa_72 and 4 others
  • Laddar…
The middle of the beam, and then in with cc30 and 22spångolv,
 
  • Like
Anonymhusbyggare
  • Laddar…
Q
  • Like
Tompa_72 and 2 others
  • Laddar…
I can recommend my own thread on how I did it. Turned out excellent! In addition to what is visible in the pictures, I added 22mm flooring chipboard + 22mm grooved chipboard, reinforcement mesh + self-leveling compound. It's sturdy today!

Edit; in the largest compartment in the second-to-last picture, we made an 85mm hole I believe it was, when the pipe was in place, I also put pieces between the beams along the pipe for additional support

https://www.byggahus.se/forum/threa...ag-i-badrum-bilder-finns.520412/#post-5792793
 
  • Like
Anonymhusbyggare
  • Laddar…
A
Thanks for the links!

cc300 is the plan 🙂, but we need a plan for the drainage before we proceed.

Q qvirre said:
If you have space, I would lay a new beam parallel next to the old one to ensure that the tiles don’t crack later. That is, I wouldn’t rely on the old beam at all as it has such large notches in the wrong places.
We don’t have the option to lay a new one all the way along the old one. Large parts of the floor outside the bathroom would have to be removed, which we’d rather avoid.

Is it better or worse to set another one parallel but attached to the short beam under the bathroom wall, which in turn is attached to the damaged beam, than to reinforce it in some way?
 
I have had to cut open the floor outside the bathroom myself to install new beams from the outer wall to a basement wall under the bathroom for support. Feels stupid to take a chance.
 
Ceiling view showing wooden joists and plumbing pipes being installed, illustrating renovation work to move plumbing across. Floor joists with a pipe running through, part of a plumbing relocation project, visible tools and materials on the floor.

Also made a hole straight through the beams to move the drainage across.
 