I need to hole saw through some ribs in the intermediate floor (220) to get the ventilation pipe (105) in the right compartment, is it okay if I do this directly above a wall that is 120 (the core wall).
Norrl.
Norrl.
Here you can read a bit about hole cutting in floor structures http://www.traguiden.se/TGtemplates/popup1spalt.aspx?id=1251
Well, you're not supposed to drill directly over the support. Looking at the link provided by Ola78 ("rules of thumb"), you can see that the maximum hole diameter for a 220mm joist is 110mm (h/2). The hole should be centered and at least 440mm from the support.
If you're going to reinforce it, I think the best way is to splice/reinforce the joist since it's the bending moment over the support that the joist needs to withstand, which is weakened by the hole. For example, plywood on each side of the joist, glued and screwed/nail. In a pattern like a die (5) on either side of the hole (but with more screws/nails between the two dots to the right and left of the center dot). And a splice length of about 120cm. Note that I'm just estimating above.
Maybe there is someone more knowledgeable who can confirm or correct my thinking...
If you're going to reinforce it, I think the best way is to splice/reinforce the joist since it's the bending moment over the support that the joist needs to withstand, which is weakened by the hole. For example, plywood on each side of the joist, glued and screwed/nail. In a pattern like a die (5) on either side of the hole (but with more screws/nails between the two dots to the right and left of the center dot). And a splice length of about 120cm. Note that I'm just estimating above.
Maybe there is someone more knowledgeable who can confirm or correct my thinking...
Member
· Västerbottens län
· 18 058 posts
I am against having at least 440 mm from the support. It is better to make holes at the support.
However, one thing that applies to a whole floor structure is that the floor/beams on the other side of the heart wall act as a counterbalance and reduce deflection. A whole floor beam gets a "fixed clamping" over the heart wall and is negatively affected by the hole cutting.
Make holes by the wall, it holds, if you're nervous, glue-screw 45x45 on both sides at the top and bottom.
Protte
However, one thing that applies to a whole floor structure is that the floor/beams on the other side of the heart wall act as a counterbalance and reduce deflection. A whole floor beam gets a "fixed clamping" over the heart wall and is negatively affected by the hole cutting.
Make holes by the wall, it holds, if you're nervous, glue-screw 45x45 on both sides at the top and bottom.
Protte
Member
· Västerbottens län
· 18 058 posts
Look what a "masonitbalk" looks like.
Protte
Protte
If the beams continue beyond the end wall, i.e., if they extend over 2 spans, then the position at the end wall is the absolute worst point to weaken the beams. It is where the greatest stress, tension, occurs.