31,552 views ·
22 replies
32k views
22 replies
Does this truss need support from a load-bearing wall?
Does this truss need support from a load-bearing wall, or is it self-supporting?
I can add that the manufacturer does not respond to emails...
The truss: https://www.lundqvisttakstolar.se/wp-content/uploads/2016/09/6045-22-1.pdf
The image explains what I mean:
I can add that the manufacturer does not respond to emails...
The truss: https://www.lundqvisttakstolar.se/wp-content/uploads/2016/09/6045-22-1.pdf
The image explains what I mean:
Member
· Blekinge
· 10 117 posts
A bit odd in appearance, but the idea is probably that it should be self-supporting over about 7 meters. What is the snow zone?
Self-builder
· Stockholm
· 2 705 posts
Is it divided like the image, yes unfortunately it needs to be, above or below.
Self-builder
· Stockholm
· 2 705 posts
Point 7 refers to a setup/support, almost missed it when I was building my garage.
Member
· Blekinge
· 10 117 posts
It is a bit tricky to enter the calculation of a truss without knowing the parameters. They have obviously used a known calculation program. If you compare with Träguiden's data on a W-truss with a roof slope of 1:2 (27 degrees), the upper and lower frames have the same dimensions, but reversed. The struts, on the other hand, are slimmer than Träguiden's, 70 mm instead of 145. It's still in the same ballpark.
Member
· Blekinge
· 10 117 posts
6 m self-supporting is no problem. In Skåne, you can at least reach 11 m.
7 should be a reinforcement. It is probably the outlines in 1 and 5 that are the support points.
Member
· Blekinge
· 10 117 posts
With a W-truss, 11 m is probably a realistic limit for Skåne. With other constructions, there are almost no limits other than economic ones.
Member
· Blekinge
· 10 117 posts
It might not be what I call a W-truss, but sure, there's almost no limit to the span of a truss.