Hello everyone.

What do you think of this construction method for a 1970s house?

# Foundation:
surface layer
40 concrete screed
60 cellular plastic
100 structural concrete
150 gravel fill

# Exterior wall from the outside:
brick
20 air gap
70 mineral wool
150 aerated concrete

# Interior wall:
150 aerated concrete, resting on the structural concrete

# Floor structure from the top:
surface layer
chipboard
200 insulation
battens
gypsum board with vapor barrier

# Roof structure from the top:
concrete tiles
25x38 battens
19x25 counter battens (pressure-treated)
felt yal 1200/325
17 rough boards
50 air space
2x50 min wool
50 min wool
gypsum board with vapor barrier
 
Not much to like, very common building style at the specified time...
 
A common construction. Quite sturdy and with few problem areas. However, the roof will likely need to be redone in the next few years like all houses from that time.
 
Hi,
Thank you for your responses.
What are the most common problems with such a house?
Can you get moisture problems from the ground up to the lättbetong walls? Do they absorb moisture?
 
If there are no problems after 50 years, it is unlikely that any would arise now as long as the conditions do not change.
 
  • Like
fahlis and 1 other
  • Laddar…
Yes, very logical :)
Possibly the first house, so one is a bit extra concerned since one has read a lot about moisture problems with wooden houses.
The only wood on the ground floor is 2 glulam pillars that are probably on K-concrete but there should be paper between the wood and concrete, at least according to the plan.
 
There are likely new problems with that construction.
The only issue in that case is if the aerated concrete is blue Ytong, with well-known problems related to it emitting radon.
But that's easy to check.
Otherwise, it seems solid.
 
Hello.
I've been thinking about blue concrete.
However, the owner conducted a radon measurement in 2008.
The value was 30 bq/m3 on both the ground floor and the upper floor.
Shouldn't that rule out blue concrete? Or should the walls still be checked with a gamma radiation meter?
 