Planning to place a 500-liter buffer tank in the earth cellar, wall to wall with the boiler room. The floor consists of loose gravel and soil, quite dry. Initially, I was just thinking of placing the tank on a sheet of ground insulation. Would that suffice, or should I pour 5cm of concrete? It would then involve about 80 liters of concrete. Does the substrate need to be packed somehow? I have only cast a little under the wood stove before, it was fun and turned out well, but otherwise, I don't know much about casting. What I used then was fast-setting fine self-leveling compound.
 
Or is it enough to place the tank on an 8-10mm plate maybe? Or a couple of I-beams perhaps...
 
D09
I would have made a bed of 16-32, packed, plastic, and cast 10 cm as long as the tank has feet and is already insulated

Otherwise, foam plastic in the casting and cast a form that you can frame up on with steel studs and insulated

However, I am just a DIY person with all its limitations 😄
 
Arm
 
  • Like
Joak
  • Laddar…
D09 said:
I would have made a bed of 16-32, packed, plastic, and cast 10 cm as long as the tank has feet and is already insulated

Otherwise, foam insulation in the casting and cast a form that you can frame with steel studs and insulated

However, I'm just a DIY enthusiast with all its limitations 
You want plastic between the draining layer and the slab, any particular reasons for this?
I'm about to cast in my earth cellar to have a fresh floor for a hydropress and radon separator, and I'm wondering whether I should have plastic or not.

To avoid this becoming a right thread hijacking, I should probably advise the original poster to drain, add macadam, and cast a slab over the whole floor.
In my case, I won't use any foam insulation because I want the ground to keep the earth cellar above freezing point, and there's nothing that will provide any waste heat, but you might want it warmer than that?
 
It seems like there will be casting, my dad is helping me. He has some experience, but can have some quirky ideas sometimes.
The room will accommodate one or two accumulation tanks placed at the far end. The rest will be used as a darkroom, so it will be heated.

I'm just wondering how it should be done. Shovel out two dm of the gravel, lay 10 cm of styrofoam and cast 10 cm on that with a reinforcement mesh in it? Or do I need something like single e.g. at the bottom?

What might the material cost for 6m2 if bought at Byggmax? I guess it will require 600 liters of concrete.
 
If it's well-packed underneath, I would have shoveled away a flat surface, laid isodrän, then cell plastic, and then cast. Isodrän to provide capillary breaking, but a foundation that doesn't move. Alternatively, shovel away an area larger than the tanks need, so it doesn't move afterward, edge type.

Do you have plans to cast the rest of the floor in the future?
 
Yes, it will be the whole floor. Shovel out 3 dm, then 1 dm gravel, 1 dm cell foam, and 1 dm concrete. What do you think about that? Is Isodrän better?
 
D09
Tips is to use s200 class on cell plastic, it handles long-term load better.
 
D09
Why shovel out the gravel, isn't it good if it comes up a little from the ground? :)
 
Andreas_H said:
Yes, it's the whole floor. Dig out 3 dm, then 1 dm gravel, 1 dm foam insulation, and 1 dm concrete. What do you think about that? Is it better with Isodrän?
Ah, then you just go with gravel and then foam insulation. As simple as possible. I first thought you only wanted to pour concrete under the storage tanks, hence the risk of collapse for the gravel.
 
Makk? Makadam? Gravel 16-32, could that be something? Someone said I could use gravel 0-16 to mix concrete with, and that it wouldn't result in large ugly stones on the surface, what do you think about that?
 
D09
Andreas_H said:
Makk? Macadam? Gravel 16-32, could that be something? Someone said I could use gravel 0-16 to mix concrete, and that it wouldn't result in large ugly stones on the surface at all, what do you think about that?
I'm not a concrete expert but I've only used pure materials when I've extended the concrete, for example, 2-5, 8-16, 16-32, etc.

(Perhaps 0-18 works too, have no idea but it feels wrong considering the 0 material)

Then, I haven't counted on all too fine surfaces. Could have an edge sticking up from a stone, like coarse castings under walls, etc. :)
 
Can't you simply place the tank on a pallet?
 
pelpet said:
Can't you just simply place the tank on a pallet?
And then change the foundation of the accumulator tank in a few years?? No thanks, not a good solution.

An accumulator tank should stand on an unyielding permanent foundation (concrete=great) because several steel and/or copper pipes need to be connected to it, and they don't want any movement.
 