Yes, as the title says. Is there anyone who can explain how to calculate the heat loss for ventilation if you have a flvp? Alternatively, if you can use an efficiency similar to a heat exchanger (ftx system). I have already calculated airflows and turnovers, but the final part is missing.
 
Can you measure the air temperature before and after FLVP?
 
According to NIBE Germany, the exhaust air is cooled down to approx. 0 °C.

http://www.nibe.de/nibedocuments/14174/M10941-5.pdf

A NIBE exhaust air heat pump uses the heat energy contained in the exhaust air for building heating and domestic hot water preparation. The warm exhaust air with, for example, 20 °C is passed through a heat exchanger (evaporator) and cooled down to just above 0 °C before it is released outside.
In Austria, they said that the exhaust air is cooled down by about 15 - 20 K. So if you have an indoor air temperature of 20 °C, it is cooled down to about 0 - 5 °C.

If you have a given airflow, you can then calculate the ventilation losses, I would say.
 