J justusandersson said:
Apologies for the late response. Some other things came up in between... I would go up to 90x270 on the beam.
How does 90x270 compare to 115x225? Are they equivalent?
 
No. 90x270 is significantly better. You have to go up to 165x225 to find a wider but equivalent dimension.
 
J justusandersson said:
No. 90x270 is significantly better. You need to go up to 165x225 to find a wider but equivalent dimension.
Ok, thanks for the answer, then it will be 90x270.

Another thought/question on the same topic. I am also going to create an opening for a window "under the same rafters". The idea was to use 90x225 glulam as a support beam and 90x90 glulam as side pillars, but that was when I thought it was a stud wall with wood shavings as insulation. But now that I've discovered the charm of plank walls, I want to make as small an intrusion as possible. So what solution do you recommend?

To open up according to the drawing and embed two 90x90 glulam beams as side pillars?

Or to "notch" into the plank wall for the load-bearing beam and let it rest on the plank wall, I think you could leave 3 planks on each side to rest on. That corresponds to about 30 cm on each side to transfer the loads.
 
  • Diagram depicting a window opening in a wall, labeled with laminated timber beams: 90x225 mm header, 90x90 mm side columns; wall measures 2000 mm wide.
  • Illustration of wall construction plan showing a 90x225 mm wooden beam above a window with notes on using 2"x4" planks for support.
Writing the answer on the phone so I need to be brief. The final solution is the best in principle.
 
  • Like
Viktor.J
  • Laddar…
J justusandersson said:
Writing the answer on my mobile so I have to be brief. The last solution is best in principle.
Thanks, would you say that 3 planks per side are enough as side pillars? More/less?

Once again, a big thank you Justus!
 
I think three planks will be good.
 
  • Like
Viktor.J
  • Laddar…
J justusandersson said:
Three planks I think will be good.
Many thanks for the help !
 
J justusandersson said:
I think three boards will be fine.
I did exactly as you said, Justus, and despite the heavy snow on the roof, there has been 0 mm of deflection so far.

Anyway, I am about to unload and insert the new beam into the opening in the main wall that the post was originally about :)

But I've started to think about the side columns and their attachment. One is intended to be next to the chimney, it's a "wing" built out as the current wall goes there. So from a fire safety perspective, I'm not worried, but I doubt whether I can attach the side column to the chimney.

The other column I can attach to the main wall, so that should be fine. But the question is how I handle the side column next to the chimney? If one column is attached to the main wall, the supporting beam is fixed to this, and the beam in turn can be attached to the rafters, can't it? Then shouldn't the side column next to the chimney only take vertical forces and thus not require attachment other than between the beam/side column and side column/floor?
 
Make sure the pillar is locked horizontally, at the top and bottom. Do not fasten into the chimney.
 
J justusandersson said:
Make sure the column is locked horizontally at the top and bottom. Do not attach it to the chimney.
Thanks, just as I thought, that's a relief. I've read many of your really great posts here and have understood that you prefer wood over steel, and perhaps especially not to mix them.

But I'm still curious to at least evaluate what dimension a steel beam (like an HEA type) would need to be to carry the same loads as the glulam beam of 90x270. It will build quite a lot simply put. It's not a disaster, but it would be nice to know what one might gain with a steel beam.

Thanks for all the help, Justus, a treasure trove!
 
HEA 140 corresponds to 90x270 glulam in this case. Even with cladding added, an HEA beam is significantly lower. I have nothing against steel, but especially in renovations, it can be troublesome. Moreover, it is heavy and expensive. In a new construction where you can lift in a steel beam with a crane and simplify the structure thanks to the steel, I think it is a different situation.
 
J justusandersson said:
HEA 140 corresponds to 90x270 glulam in this case. Even with cladding, an HEA beam is significantly lower. I don't mind steel, but especially in renovations, it can be troublesome. Additionally, it's heavy and expensive. In new constructions, when you can lift a steel beam with a crane and simplify the construction thanks to the steel, I think it's a different situation.
Thanks for the response. Then it will probably be HEA. Since I need about 2300mm, the price will be the same as buying a cut HEA140 as a 6m 90x270.

Can I still use 90x90 side pillars, or should I use 150x150 to match the HEA beam's "imprint" of 140mm?

Likewise, the span ensures that the weight won't be a big problem; it should weigh about 60kg.

Besides price and weight, is there any other potential complication I should consider and prevent while building?
 
There is a point in having the same width for beams and columns. There are many alternatives to 90x90, such as 90x135 or 140x140. From a load perspective, however, 90x90 is sufficient. Steel has greater longitudinal expansion than wood, so some allowance for movement is desirable.
 
J justusandersson said:
There is a point in having the same width on beam and pillar. There are many alternatives to 90x90, such as 90x135 or 140x140.. From a load perspective, 90x90 is sufficient. Steel has greater thermal expansion than wood, so some allowance for movement is desirable.
I see, thanks. In the opening, there are two trusses, the next ones rest at one end on the load-bearing wall and on the other side of the opening shows a wing on the chimney. A carpenter recommended offloading from above. That is, letting the load-bearing beam run on top of the trusses' lower arms over the load-bearing wall. Fix the first trusses to the secondary beam with fork anchors. Could this be an option? I am considering a 90x270 glulam resting on the truss near the chimney (which in turn rests on the chimney) and then letting it continue over 3-4 trusses over the load-bearing wall. Then the load from the two free-hanging trusses should be transferred down via the chimney and down to the load-bearing wall via the trusses on the other side.

The advantage of this, besides the aesthetic aspect, would be simplicity. You avoid aligning pillars and fitting a beam. And you gain more space where it is needed (in the attic it doesn't matter).

I have the ceiling joists exposed in the attic for running electricity, so I can offload in more ways if needed.

Best regards,
Viktor J
 
Last edited:
J justusandersson said:
There is a point in having the same width on beams and pillars. There are many alternatives to 90x90, such as 90x135 or 140x140.. From a load perspective, however, 90x90 is sufficient. Steel has greater thermal expansion than wood, so some allowance for movement is desirable.
what do you say Justus, would that be an option? I could also consider using the pillars, through the ceiling and insulation, to still support from above (if it is a suitable alternative).
 