Hello!

I have an old shed (about 7x8 m in size) that will eventually be renovated... but first, I was thinking of taking down a large part of the outer wall and installing two large garage doors as I need the space.

The wall, which is about 7 meters wide, should accommodate two garage doors that are 2.5 m wide...

My idea is to install a steel beam with a post in the middle. The space between the stone wall and the roof trusses is 12 cm... is that enough to fit a beam that can support the weight? What type of beam should I use in that case?

Attaching a couple of pictures.... Old shed with corrugated roof, wooden door, and cracked wall. Window with broken panes. Discussion on future renovation to add garage doors.
Old shed interior with a wooden door partially open to the outside. Sunlight creates shadows on the gravel path. Concrete wall and roof structure visible.

Kind regards,

Peter
 
Last edited:
Snow zone, roof pitch, municipality?

Will it be insulated in the future?
 
Karlskrona, yes it may potentially be insulated later on! Attaching a picture so you can see the roof slope better...

Red wooden building with visible pitched roof angle, possibly to be insulated in future; sunny day with trees and a wooden fence in the background.
 
HEA 120 is sufficient without any problem even with insulation and ceiling.
 
Thank you!
/Peter
 
Now I'm being a bit difficult, would HEA 100 have sufficed as well? It would have simplified the work considerably...
 
Yes, it does.
 
Good! Thank you
 