Installed a glulam beam about two weeks ago, approximately 4.5m indoors (replaced a load-bearing interior wall). Supported on wooden posts at each end. Angle irons are screwed between the beam and ceiling joists. Have now discovered longitudinal cracks on one side of the beam today, approximately 50-60 cm long. Not through-going. Is this normal? Could it be related to the fastening? Is it dangerous or just normal tensions?
 
I think it sounds like you have exceeded the beam's shear capacity. Which is not OK. I can't imagine it has to do with the attachment. But whether there is a risk of failure or not, I can't say. How large is the deflection?
 
There is basically no deflection, maybe a few mm, but nothing measurable with a laser level.
 
How confident are you that you have the correct dimension? Have you received calculations from a building engineer?

What is the dimension, and what does the load look like? That is, span, any load-bearing walls on top?
 
Sounds like you don't have the right dimensions for it, there should definitely not be any cracks in it. I think you should contact a construction engineer to come and take a look.
 
If there is a deflection of a few mm that is quite a lot since it is usually dimensioned so that the deflection y should not be greater than L/300. If you measure the deflection and give me the dimensions of the beam and the wood quality, I can calculate if you are overloading it.
 
3mm deflection in the middle. Dimension 360x120 4.5m L40.
L/300 gives a maximum allowable deflection of 15mm.
 
The crack is also in the middle of the beam (seen from the side). Overloading should cause a crack at the bottom.
 
Staffans2000
hebbe said:
The crack is also in the middle of the beam (seen from the side). Overload should cause a crack at the bottom.
My theory. In case of overload, the crack should occur in the middle, as the upper part of the beam is compressed while the lower part is extracted (is that the term?).

Torrspricka is another alternative.

staffan
 
Can't you post a picture of the crack so it might be easier when you see it..

// Per
 
Spontaneously, I think it sounds weak, but I am not a designer.

If we assume it's an intermediate floor, you probably currently have only a fraction of the load it should be designed for (200 kg/sqm). In practice, you only reach that load when you have the entire family visiting, but it should be designed for it anyway.
 
Crack in the middle proves that you have exceeded the beam's shear capacity.
 
It's very hard to see how the beam would be overloaded without showing any deflection. Can't the dry season create dry cracks in glulam?
I will try to upload a picture of the crack shortly.
In my opinion, a beam loaded with a distributed load has the least stress in the middle of the beam.
 
Yes, if I remember correctly from strength of materials (a long time ago), it was called the neutral line.
 
  • Like
Rickard von Essen
  • Laddar…
I
A horizontal crack in the beam’s neutral line does not at all mean exceeded load-bearing capacity. Shear cracks can appear anywhere along the beam's height, but the risk is least in the neutral layer where tensile forces at the bottom are replaced by compressive forces at the top (conversely over supports). Or rather: the risk is greatest where the change in length is greatest. And it should be within 1/4 of the height from the respective lower or upper edge to the respective edge.

Another and more likely explanation (since the beam does not bend downward and the crack is not through-going) is that it is a manufacturing defect due to a lack of bonding between the lamellas.
_______________________
Byggaren
 
Vi vill skicka notiser för ämnen du bevakar och händelser som berör dig.