I am working on a garage project with a gable roof with a span of 7.5m, snow zone 1.5.
The basic idea was to have a load-bearing interior wall in the middle, so the span is 3.25m per section.
The studs in the load-bearing interior wall are 45x95mm cc 60 with a 45mm thick top plate on which the rafters rest.
If I now want to replace the load-bearing interior wall with posts at about 120cm instead without paneling, how much do I need to increase the dimension of the top plate then?
I have searched everywhere but can't find a table or explanation on how much the load-bearing capacity decreases if I increase the distance between the posts instead of the original classic interior wall with cc60?
I spontaneously think 95x95 posts with double nailed 45x145 on cc120. Will that work, or can I reduce the dimension further?
Should be about 3.75 m?
There are some missing details to be able to calculate it properly. What do the roof trusses look like? What will the loft be used for etc. Normally, double glued 45x95 beams should suffice. Note that freestanding pillars must be dimensioned considering the risk of buckling.
Should be about 3.75 m? There are some missing details to be able to calculate it properly. What do the roof trusses look like? What will the loft be used for etc. Normally, double screwed and glued 45x95 should suffice. Note that free-standing posts must be dimensioned with consideration for the risk of buckling.
I was thinking of using rafters 45x145 C24 and a central beam/load-bearing beam/main beam with 2 glued vertical 45x145s with posts at cc 120. I would have liked to be able to roll pallets between the posts though, so it needs to be about 130 between the posts.
Your idea of placing the rafters directly on the posts at cc 120 is good in one way, but it's not flexible if you want to move a post for some reason, perhaps?
45x145 C 24 with a span of 3.75 meters in snow zone 1.5 is a bit undersized. With c/c 600 mm, 45x220 is needed according to my quick check. You can place double screw-glued 45x220 on c/c1200 mm (or 1300 mm) with the same result.
45x145 C 24 with a span of 3.75 m in snow zone 1.5 is on the flimsy side. With c/c 600 mm, 45x220 is needed according to my quick check. You can use double screw-glued 45x220 on c/c1200 mm (or 1300 mm) with the same result.
Ok, so you think the calculation according to the picture is a bit weak, do I interpret you correctly then?
My problem is that the ceiling height at the edge of the shed roof becomes extremely low, which is my problem.
You mean that 2 screw-glued roof beams 45x220 C24 directly on posts on cc 130 would work? (Without a load-bearing beam)