Hi,
I need advice on how many noggings are needed for this joist construction.
The architect didn't include any - but I still think cross braces or install noggings.
The question is just where and how many?
Best regards,
Hobbit
 
Mikael_L
Is it the upper floor?
Is it a glulam beam drawn across the floor in the middle of the span?
What is the total span width?
Do you have a bathroom that is going to have tiles somewhere there, and do you have any special loads?
 
  • Like
Yngwie74 and 1 other
  • Laddar…
1. Is it the upper floor?
2. Is there a glulam beam drawn across the joist in the middle of the span?
3. What is the total span?
4. Do you have a bathroom that needs tiling anywhere there, and do you have any special loads?
1. Yes, upper floor
2. No, an HEA 260 steel beam
3. 6410
4. Yes, in the upper right dormer
 
Mikael_L
Hobbit said:
2. No a HEA 260 steel beam
Yes indeed, glulam, steel beam, hjärtvägg whatever... :)
But you kindly answer exactly the question I ask, *hehe*

With 220x45 in C24 and glued 22mm chipboard flooring you should have sufficient stability with a span of 3200 per section. I don't think you actually need blocking or bracing.
Not sure if I would bother myself. :)

But if you decide to do it, one row of blocking per section, in the middle of the section, should suffice very well.

Here's how I did it where I had a span of about 3800
http://www.byggahus.se/showthread.php?t=155701
 
The one who asks shall receive an answer - of course. ;)

I also don't think the beams can twist.
I just want to distribute the load as much as possible.
The upper floor will be a loft that my kid will get as his first bachelor pad. And you know what a group of teenagers might come up with - like jumping on a trampoline indoors..............
So sure, it might be a bit excessive with noggins and 170 walls instead of 145, and HEA 260 instead of HEA 240 - but when I build, I build for eternity, you know .....:D
 
Mikael_L
You don't use blocking/cross-bracing to prevent the beams from twisting, but to achieve a more rigid floor. The cross-bracing forces the adjacent beams to take some of the load, thereby reducing deflection under point loads.

If you really hate the idea of even suspecting any sway, then you should block/cross-brace your floor structure, preferably with a row in the middle of each bay, i.e., about 1.6 meters from the outer wall. But don't forget to screw and glue the chipboard flooring, this does a tremendous amount to reduce sway.
 
Larsa said:
Hijacking the thread.... Regarding glued flooring panels. Should they be glued to the joists or just to each other (tongue and groove)?

---
I am here: [link]
They should be glued to the joists and in the tongue and groove. And screwed.

Otherwise, I have roughly the same spans as the original poster and no noggins...that's a relic from the time before flooring panels and screw-gluing. I don't experience any sway despite small children jumping and running around. I would probably spend time and money to reduce the center-to-center distance to 30 cm across the entire joist if there was a risk of young people breaking the flooring panels or putting them into motion. Alternatively, lay a self-supporting 25mm pine floor across the joists to further secure it.
 
Mikael_L
Larsa said:
Hijacking the thread.... Regarding glued floor particle boards. Should they be glued to the joists or just to each other (tongue-and-groove)?]
Both. Download the installation instructions for your specific floor particle boards and follow them. They usually specify everything, from the type and amount of glue to where it should be applied.
 
OT: Which architect helped you? Can you recommend them? I'm planning to extend the upper floor a bit and will soon need help with drawings.
 