We are applying for a building permit to install a patio door (140cm) on the red-marked wall. Our neighbor has done exactly the same thing on exactly the same type of house, but it was so long ago that she doesn't remember if it was load-bearing or not. And I don't know how to read this drawing. Is the red-marked wall load-bearing or not? And if it is load-bearing, could I possibly get help with calculations, etc. that I can send to the municipality? 
Member
· Stockholms län
· 15 posts
Yes, exactly a "felvänt" house like that 
Member
· Stockholms län
· 15 posts
I don't think it's load-bearing either, but I want to be on the safe side. 
Member
· Blekinge
· 10 117 posts
From the drawings, the floor plan of the upper floor and the sectional drawing, it is evident that the trusses are oriented the "wrong" way, and therefore the outer wall in question is not load-bearing. The section also specifies which interior walls are load-bearing.
Member
· Stockholms län
· 15 posts
Thank you 