Fire protection EI30 garage in the basement
We have a house with a garage in the basement. A fairly large part of the basement has an "open plan" towards this garage (storage, workshop, etc.) Now we are considering extending the house on both levels. It will then be a larger garage in the basement. Preferably, we don't want a door/wall between the new and old part of the garage. I have understood that EI30 is required between the garage and living spaces. I assume this also affects the existing part of the garage? All walls are built with masonry, so it should be OK. But I am unsure how to evaluate the floor structure. It consists of 200mm high joists with mineral wool insulation between. (I believe the insulation is 95mm). Below that is 18mm of rough plywood and 9mm of gypsum board. How can I find out if this meets EI30 / REI30? Most examples I find are about walls or new floor construction. Grateful for tips!
Self-builder
· Stockholm
· 10 104 posts
Are you sure they don't require IE60?N nomis said:We have a house with a garage in the basement. A fairly large part of the basement has an "open floor plan" towards this garage (storage, workshop etc.)
Now we're considering extending the house on both floors. It will then become a larger garage in the basement. Preferably, we don't want a door/wall between the new and old part of the garage.
I understand that EI30 is needed between the garage and the living areas. I assume this also applies to the existing part of the garage?
All the walls are masonry, so that should be OK. But I'm unsure about how to assess the floor structure. It consists of 200mm high beams with mineral wool insulation in between. (I believe the insulation is 95mm). Below that is 18mm tongue and groove boards and 9mm plasterboard. How can I find out if this meets EI30 / REI30? Most examples I find are about walls or new construction of floor structures.
Grateful for tips!
Double plasterboard and Rockwool are usually the easiest solution.
Thanks for the reply!
However, still confused... Found this on träguiden after I created the thread:
källarbjälklag with beam of konstruktionsvirke or glulam, ≥ 45x170 (VB1974 or VB3100), center distance ≤ 600 mm, on the top side equipped with subfloor of ≥ 22 tongued floorboards or 23x95 underlagsspont (VB2055) and on the underside equipped with at least 9 mm cladding board (density ≥ 450 kg/m3) against glespanel 22x70 (VB0804) c 400 mm alternatively 17x95 underlagsspont (VB2049), meets the requirement for fire technical class EI 30.
However, still confused... Found this on träguiden after I created the thread:
källarbjälklag with beam of konstruktionsvirke or glulam, ≥ 45x170 (VB1974 or VB3100), center distance ≤ 600 mm, on the top side equipped with subfloor of ≥ 22 tongued floorboards or 23x95 underlagsspont (VB2055) and on the underside equipped with at least 9 mm cladding board (density ≥ 450 kg/m3) against glespanel 22x70 (VB0804) c 400 mm alternatively 17x95 underlagsspont (VB2049), meets the requirement for fire technical class EI 30.
Self-builder
· Stockholm
· 10 104 posts
Click here to reply
Similar threads
-
Brandskydd till utbyggnad av Willabgarden uterum nära garage
Utbyggnad och tillbyggnad -
Hjälp: Garageport EI30
Attefallshus, friggebod, garage & andra småhus -
brandskydd EI30
Isolering -
Ei30 oisolerat garage
Utbyggnad och tillbyggnad -
I need a drawing of a fireproof garage wall EI30
Building Materials and Construction Technology