I have made a slightly too large hole around a pipe in the bathroom. Säker Vatten says Max 2mm, I have 5mm on one side of the pipe. What can I fill it with to comply with Säker Vatten?

I will have waterproofing and tiles on the walls.
 

Best answer

Check the installation instructions for the waterproofing membrane you are going to install. For example, here's what it says in Kiiltos:

Text instructions detailing a maximum 2 mm gap between wall/floor board and pipes, suggesting using soft sealant, avoiding silicone.

At some point, I have seen that cement-based filler should be used.
 
  • Like
Derbyboy
  • Laddar…
Perfect, then it's clear as day!
 
  • Like
Derbyboy
  • Laddar…
D
Thank you!
 