Hello
I am renovating an old house from 1938, as usual with old houses it has been expanded to the right and left, and small things become big challenges.
Now I am a bit stuck in the “thinking” on the upper floor and need advice.
The idea is to make a large bathroom there with underfloor heating and tiles. What worries me is that the beams, which are almost five meters (4950x3960), become shaky and that the tiles crack in the joints. I don't know what to do as I don't want it to become too heavy either. Worth mentioning is that there is no load-bearing wall underneath.
I have been advised that cc 30 (45x220) and noggings are sufficient, the question is if it is enough?. I would rather put in a bit more work so that it’s done right than for it to become “fiddly”.
Thanks in advance :)
Renovation of an old house; exposed wooden floor joists with electrical wiring. Walls partially covered with insulation. Planning for a bathroom installation. Floor joists of an old house under renovation, showing wooden beams, electrical wires, and plumbing pipes on a partially constructed floor. Wooden floor beams of an old house under renovation, showing exposed joists and wiring, with a focus on structural concerns for a bathroom upgrade. Floor plan of a house's upper floor, showing rooms including a 12m² bathroom, hallway, and bedrooms, with dimensions and annotations in Swedish.
 
Åsa Lund
There are quite good instructions from BKR regarding substrates for tiles.
A completely different comment. Is it good to have a sink under a slanted ceiling?
 
Åsa Lund Åsa Lund said:
There are quite good instructions from BKR regarding substrates for tiles.
A completely different comment, is it good to have a washbasin under a slanted ceiling?
Hi Åsa
Apologies for the old drawing, the toilet and washbasin have swapped places. It's not visible on the drawing, but the ceiling height is quite high, so the sloped ceiling starts at 1.60. My problem is not making it stable, but more how to solve it in the best constructional way :)
Regards
 
22mm chipboard floor and then floor gypsum glued with Ardex S48 or similar, then filler with reinforcement, then it "should" hold well.
 
nino nino said:
22mm chipboard flooring and then floor gypsum glued with Ardex S48 or similar, then leveling compound with reinforcement should "hold" it
Sounds reasonable, but as mentioned, I am planning to have underfloor heating with pipes beneath the tiles, and the ceiling height is a problem, ending up at about 2.30m
Regards
 
The hose is sparse between the joists but there's a lot to be heated...
Electric heating then? It can be laid in the compound without significantly affecting the thickness.
 
I am also thinking about electric heating. You control it completely separately, and you can have nice heat even in late spring and early autumn without affecting the rest of the system.
 
Åsa Lund
I think we have a waterborne system that is in 15 mm screed
I believe we have LK
 
  • Like
Birka69
  • Laddar…
Åsa Lund Åsa Lund said:
There are waterborne systems that are embedded in 15 mm screed, if I remember correctly.
I think we have LK
Yes, but it's 15mm to cover the hose, then you screed as on regular chipboard
 
nino nino said:
The hose is sparse between the studs but there will be a lot to heat...
Electric heating then? It can be laid in the filler without significantly affecting the thickness
Worth considering, but I was thinking of having water radiators and was planning to run hose everywhere, so I thought I might as well do the bathroom too, :)
 
It will never be really good with 45x220 and c/c 300, as the span is too long. In this case, noggins won't help. It's a bit hard to see from the images what the most appropriate action is. There are two strategies. One: Insert new glulam beams between the existing beams or Two: Reinforce the existing beams by screw-gluing more material onto them.

140x225 glulam c/c 600 with screw-glued particle board on top meets the requirement.
 
  • Like
Birka69
  • Laddar…
J justusandersson said:
It will never be really good with 45x220 and c/c 300, because the span is too long. In this case, noggins won't help. It's a bit difficult with the help of the pictures to see what the most suitable action is. There are two strategies. One: Insert new glulam beams between the existing joists or Two: Reinforce the existing joists by screw-gluing more material.

140x225 glulam c/c 600 with screwed plywood on top meets the requirement.
The original joist is today screw-glued/aligned with 45x220, if I screw-glue 45x220 on the corresponding/opposite side of the original joist I get about 140... or do I need glulam/Kerto?
Best regards
 
3 x 45x220 C 24 c/c 600 screwed and glued is sufficient if you also have a screwed and glued particle board on top.
 
  • Like
Åsa Lund
  • Laddar…
J justusandersson said:
3 x 45x220 C 24 c/c 600 screwed and glued is sufficient if you also have screwed and glued chipboard on top.
Thank you, that was the answer I was looking for :)