Reinforcing floor joists when running pipes through the beams?
Page 1 of 2
This has been brought up a bit, but I don't really think I've seen the answer to my question.
I will want to run quite a lot of VP conduits for electricity across the existing floor joists. 9" x 2" with cc about 600mm (floor level above basement in a house from the 1930s).
I have seen recommendations about where to make the holes (but have also read contradictory info). Typically in the middle or closer to the support.
If I choose to put a sheet of plywood, screw-glued, on each side where I make holes (quite a lot of conduits that need to go through in some places), can I then "ignore" the recommendations about where to make the holes? Or is this reinforcement not good enough?
The holes will be about 20mm, and there is some rule about the distance between the holes that I don’t remember but will follow. Holes in the center of the beams, not at the edge. I will have lots of circuits for my new kitchen so there will be quite a lot of conduits to run, so many holes it will be....
I will want to run quite a lot of VP conduits for electricity across the existing floor joists. 9" x 2" with cc about 600mm (floor level above basement in a house from the 1930s).
I have seen recommendations about where to make the holes (but have also read contradictory info). Typically in the middle or closer to the support.
If I choose to put a sheet of plywood, screw-glued, on each side where I make holes (quite a lot of conduits that need to go through in some places), can I then "ignore" the recommendations about where to make the holes? Or is this reinforcement not good enough?
The holes will be about 20mm, and there is some rule about the distance between the holes that I don’t remember but will follow. Holes in the center of the beams, not at the edge. I will have lots of circuits for my new kitchen so there will be quite a lot of conduits to run, so many holes it will be....
Here you can read about the recommendations for hole cutting:
https://www.traguiden.se/konstruktion/konstruktiv-utformning/stomme/bjalklag/barformaga--bjalklag/
Here you can read about how to make a reinforcement:
https://www.traguiden.se/konstrukti...lag/bjalklag--generellt/forstarkning-vid-hal/
https://www.traguiden.se/konstruktion/konstruktiv-utformning/stomme/bjalklag/barformaga--bjalklag/
Here you can read about how to make a reinforcement:
https://www.traguiden.se/konstrukti...lag/bjalklag--generellt/forstarkning-vid-hal/
Self-builder
· Stockholm
· 10 105 posts
Can't you run the pipes through the studs to the basement ceiling?
Member
· Blekinge
· 11 708 posts
I would screw-glue long strips of plywood on both sides. The beams must have smooth sides. Then you can drill the holes through both the plywood and the beam. 17 mm diameter should be enough. Every mm counts in weakening.
Ahh, maybe it was unclear. This is a renovation/rebuilding, so the raw wood is in place. Replacing the entire floor on the upper floor in conjunction with moving the kitchen, which opens up and gives me access to the joists.H huggan said:
That's exactly what I want to do but I'm unsure how much it will help.T Thomas_Blekinge said:
How smooth is smooth? They're not planed beams but also not hacked with an axe. I realize as you write this that it could become a problem. That is, the gluing won't be strong enough, and it will only be the screws handling the load (to use layman's terms).
Nailed raw boards on the underside and later screw-glued particle board on the top should also help a bit, I hope.
As a layman's know-it-all, I intuitively say that the sheathing on the underside, across the beams, doesn't bear a thing. Imagine a crack appearing in a beam, on the underside of course, how is it supposed to be relieved by your sheathing? The sheathing just splits apart there. Or cracks between two nails. But of course, there will be a "hammock effect" sideways, so your beam won't collapse. Silly, I watched a YouTube film a long time ago with a "rambling rant" by an American who showed how such relief should be done. But that doesn't help you, here and now.
In the past, one might have made nail joints with two planks, half the beam thickness, length: half a meter on each side of the hole. And then nail from alternating sides in a grid pattern so the nails don't meet.
Short answer: Think "nailed joint with wooden lash" https://www.traguiden.se/konstrukti...xempel/bostadshus/spikad-skarv-med-tralaskar/
In the past, one might have made nail joints with two planks, half the beam thickness, length: half a meter on each side of the hole. And then nail from alternating sides in a grid pattern so the nails don't meet.
Short answer: Think "nailed joint with wooden lash" https://www.traguiden.se/konstrukti...xempel/bostadshus/spikad-skarv-med-tralaskar/
You should absolutely not make holes in the bottom or top edge since the most forces are there. Consider why HEA and IPE beams have their shape? It is because the greatest forces are at the top and bottom of a beam, hence the wider flanges to take up forces while the web can be narrow.