Hello!
I am planning to build an upper floor on our existing single-story house.
The floor joists on the upper floor will span a length of 9 meters, and on the ground floor I will be installing load-bearing walls and steel beams (18 cm H-beam), but to minimize the number of steel beams I want to know the maximum distance for the supports, i.e., the span width.

Can a normally loaded floor with 220 mm joists handle a span of 4.5 m?

Is an 18 cm high H-beam enough for support? Glue-laminated beams take up so much space in the ceiling. I don't want to notch the joists. Too much work! :)

The building permit drawings are available at http://hem.fyristorg.com/warnby/bostad/

I have not yet arranged for structural drawings and plan to attempt my own drawing first to see what the building committee says.

Thankful for answers and advice!
/Marcus
 
Know a house manufacturer that uses 45x220 with cc 600 up to 4.2 m. With cc 300 up to 4.8 m.
 
Thanks for the tip, but can you name the house supplier?

Sounds good with 4.2 m. What classification is the timber? K24?

/M
 
Mikael_L
According to your thread, it seems like you can have a 9-meter house if you splice the floor joists? Apparently, as I understand Träguiden, a floor joist should not be longer than 7 meters.

In that case, I'm thinking I would lay a 5-meter length from one direction and one from the other and then nail them together parallel. The c/c distance will still be 60 cm, but on one half of the house, it shifts slightly to the side. Should work, right? Made a little sketch of what I mean.
 
  • Diagram illustrating the construction plan for floor joists spanning 9 meters, with joists of 5m, c/c 60, and support from 16cm H-beams and walls.
macaroni said:
Thanks for the tip, but can you say the house supplier?

Sounds good with 4.2 m. What classification is the timber? K24?

/M
The house supplier doesn't matter, but it's one of the biggest.
The timber is K24.
 
  • Like
carlarvid
  • Laddar…
By screwing and gluing floor chipboard directly to the joists, you can increase the span. We have 5.3m/cc600/220mm K24 at one place in the house. This has been calculated and approved by the engineer.
 
I have also heard about screwed and glued. But what do you have on that floor? No heavy sections like wardrobes, pianos or similar, I assume?

/M
 
macaroni said:
I have also heard about the screwed and glued method. But what do you have on that floor? No heavy parts like wardrobes, pianos, and similar, I assume?

/M
No, nothing particularly heavy, but that question never came up. I assume it accounts for a standard load. We wanted to avoid c/c400 at all costs. That's why this solution came up.

You should still check with a structural engineer or building engineer. Alternatively, use Kerto-beams.

http://www.byggahus.se/forum/byggmaterial-byggteknik/42118-vad-aer-en-kerto-balk.html
 
I have 4.5m cc300, 400, and 600 depending on the placement. Sure, there is a little flex with cc600 but not so much that it bothers...
 