Hi,

We are going to demolish a load-bearing wall in our house.

The house is 9m wide, 16m long, and it is the main wall that is to be opened up. The roof trusses are set at cc1.2m intervals.
The opening we want is about 4.7m.
We have snow zone class 3.

I have received a calculation that we need a glulam beam with dimensions:
140x540 or 115x630 quality GL32c

Unfortunately, the beam is too tall, so we will need to switch to a steel beam, for example, HEA.
I have been given an estimated dimension for an HEA 220 (22cm high and 18cm wide).

Is there anyone who can help me with calculating or alternatively saying if the basis is reasonably sound?

Regards,
Sebastian
 
The glulam and steel dimensions do not quite match each other. Glulam 140x540 corresponds most closely to HEA 260. If you compare in the other direction, HEA 220 (which is 21 cm high and 22 cm wide) corresponds more to 140x450. The sizing feels a bit over the top, but one needs access to a sectional drawing to say it with certainty.
 
  • Like
BirgitS and 1 other
  • Laddar…
J justusandersson said:
Glued laminated timber and steel dimensions do not quite match. Glulam 140x540 corresponds most closely to HEA 260. If you want to compare the other way around, HEA 220 (which is 21 cm high and 22 cm wide) corresponds more closely to 140x450. The dimensioning feels a bit excessive, but you need to have access to a sectional drawing to say that with certainty.
J justusandersson said:
Glued laminated timber and steel dimensions do not quite match. Glulam 140x540 corresponds most closely to HEA 260. If you want to compare the other way around, HEA 220 (which is 21 cm high and 22 cm wide) corresponds more closely to 140x450. The dimensioning feels a bit excessive, but you need to have access to a sectional drawing to say that with certainty.
Hello,

Okay.
I have included a sectional drawing as well as a floor plan. On the floor plan, I have circled the wall that should be removed.
Thinking of placing the steel beam on studs/glulam with dimensions 115x115. Or does the steel beam need to be placed on a steel stud?
 
The house has truss rafters that only rest on the outer walls. There are no load-bearing interior walls on the ground floor. You don't need a beam. Who gave you that advice?
 
  • Like
BirgitS
  • Laddar…
J justusandersson said:
The house has truss rafters that only rest on the outer walls. There are no load-bearing partitions on the ground floor. You don't need a beam. Who gave you that advice?
I think it's a bit strange that it's mentioned in the technical specifications according to the attached image below. Where it specifies that the load-bearing inner wall is made of studs and building board.

Technical document detailing construction specifications, highlighting materials and dimensions for load-bearing interior walls, foundation, and water insulation.
 
It is just sloppily filled in. Check what it says about takstolar.
 
J justusandersson said:
It's just carelessly filled out. Check what it says about roof trusses.
Hi,

I have done that. And I think it's very vague.
It says you might need a load-bearing wall.
But not in clear text when you need it…
 
K Kane said:
I think Justus means what is written about your roof trusses.
Yep, almost thought so. But there's actually nothing about them in my technical…
 
They had skipped that detail about the truss type. The technical description is filled out by someone who isn't particularly knowledgeable. Disregard it. If the trusses look like those in the section drawing, you don't need a supporting beam.
 
J justusandersson said:
They had skipped that detail about the truss type. The technical description is filled in by someone who is not particularly knowledgeable. Disregard it. If the trusses look like they do in the sectional drawing, you don't need a beam support.
Hi,

Sorry for questioning all the time, but I get a bit worried, it was a construction engineer who said I needed a beam support.

Dimensions of truss:
Bottom chord = 50mm x 130mm

Diagonal members have different designs. I'll include pictures of them as well.
The outermost members consist of 2 boards and 1 stud that are nailed together.
2 boards measuring 23mm x 100mm and 1 measuring 50mm x 100mm
The innermost members consist of 2 boards with dimensions 23mm x 100mm

Top chord = 50mm x 150mm

I really appreciate the help!

Best regards,
Sebastian
 
Forget the support beam. These trusses don't require one.
 