I have received quite good help with load calculations and sizing beams for a planned sunroom construction from Moelvens' calculation software for glulam beams. BUT what is an acceptable deflection for a glazed sunroom really? 0 mm is out of the question. Is this stated in the installation description of the glass section, or where should I look for the information?
According to my calculation result with snow zone 3.0, I can choose to accept anything between 1 and 18 mm deflection. 18 mm sounds outrageous, but 1 mm would, on the other hand, require a 115x630 mm beam, and both the wallet and the design manager aren't too pleased
Where to look?
According to my calculation result with snow zone 3.0, I can choose to accept anything between 1 and 18 mm deflection. 18 mm sounds outrageous, but 1 mm would, on the other hand, require a 115x630 mm beam, and both the wallet and the design manager aren't too pleased
Where to look?
Member
· Norrbotten
· 3 390 posts
Thank you for your response!
It would be 10 mm in my case, but there might be a difference between a floor joist and the beam above a patio section?
I have managed to read in some other suspicious documents on the internet that 10 mm is the maximum when glazing balconies. The question is how much flexibility there is in the profiles of the glazing systems? If they become rigid, it will either be impossible to open/close or directly result in broken windows.
It would be 10 mm in my case, but there might be a difference between a floor joist and the beam above a patio section?
I have managed to read in some other suspicious documents on the internet that 10 mm is the maximum when glazing balconies. The question is how much flexibility there is in the profiles of the glazing systems? If they become rigid, it will either be impossible to open/close or directly result in broken windows.
Member
· Norrbotten
· 3 390 posts
Good evening!
Of course, it's a thought, but there's a bit of a lack of space. On the other hand, it might balance out, to accept a bit more deflection and thereby choose a smaller glulam beam. I'll do some calculations on that...
Of course, it's a thought, but there's a bit of a lack of space. On the other hand, it might balance out, to accept a bit more deflection and thereby choose a smaller glulam beam. I'll do some calculations on that...
Member
· Norrbotten
· 3 390 posts
Found in Santex's description for vikdörrspartierna "The glulam beam shall have a camber of 3 mm in tolerance at the top edge." A bit amusing language, but should it be interpreted as a maximum of 3 mm sagging (what is cambering?).
http://www.santex.se/kampanjer/nyheter/SantexProduktinfo_vikdorrar.pdf
But it may vary between different brands and models
Possibly the sliding door parties can handle 7 mm? http://www.santex.se/media/58702/star skjutbara partier.pdf
http://www.santex.se/kampanjer/nyheter/SantexProduktinfo_vikdorrar.pdf
But it may vary between different brands and models
Possibly the sliding door parties can handle 7 mm? http://www.santex.se/media/58702/star skjutbara partier.pdf
Member
· Norrbotten
· 3 390 posts
Now I received a response from Skånska byggvarors customer service and they had an 8 mm limit.
Member
· Norrbotten
· 3 390 posts
Member
· Norrbotten
· 3 390 posts
Sounds expensive 
Member
· Norrbotten
· 3 390 posts
Have not yet ordered any beams and have not received the building permit either. Could lightweight beams (like masonite beams) be an option in a sunroom environment (unheated in winter)? Such beams have a significantly lower self-weight, which should be positive for the overall load case.
Click here to reply
Similar threads
-
Nyinstallerad dörr skevar - vad är acceptabelt?
Fönster & Dörrar -
Steel beam in old log house - Deflection and sizing.
Building Materials and Construction Technology -
Nymålad lägenhet - är detta acceptabelt?
Färg, Måla & Tapetsera -
Nylagt golv sviktar vid listerna - acceptabelt?
Golv -
Conversion of glulam beam to IPE steel beam regarding deflection
Building Physics